The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 196 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#32851 - 01/04/04 01:56 PM Subpanel Calculation
Nebraska Offline
Junior Member

Registered: 01/03/04
Posts: 1
Loc: Grand Island, NE, USA
I recently added a sub panel to my house It contains 3 15 amp breakers, 2 15 amp tandem breakers, 1 20 amp breaker and 1 2 pole 30 amp breaker for a water heater, all the 15's and the 20 are for general purpose receps. How do you calculate the size of breaker to put this sub panel on. Taking 80% of all the breakers added together just doesn't seem right, maybe it is though. Please help me. Thank you.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#32852 - 01/04/04 02:16 PM Re: Subpanel Calculation
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
You got the cart before the horse. First, you compute the combined loads, using diversity factors allowed by the NEC. Second, you choose a panel of a size adequate for the loads just computed. Third, you choose a feeder of ample size. Fourth, you choose a circuit breaker sized to protect the feeder and panel.

Or, take the shortcut: size the breaker for the size of the new panel (usually 100 or 60 Amps)and feed with 100 or 60 Amp wires.
_________________________
Earl