#32450 - 12/23/03 07:44 AM Neutral on back up generator
Rob Offline
Member
Registered: 12/22/03
Posts: 15
Loc: New York
Hi my trade is HVAC.One of my heating customers has the following senario.
5,000 watt generator.
Unused welder feed in his garage, 2 hots and a ground.The generator has a NEMA round 4 conductor 220 output.He wired the generator
to the old welder feed which now feeds the
transfer switch panel breakers. He did not hook up the neutral because there was only the ground. Customer turns off main to house
starts generator, has 220 volts across 30 amp
breaker, 120 to ground off both legs.
Turns on breaker to living room and the TV
smoked. Why? Isnt the ground and neutral one and the same at the generator. I told him he needs a seperate neutral at the generator too.(yes or no) He is calling an electrican
and learned his lesson on wiring generators.
Thanks for your explanations.
Top
Work Gear for Electricians and the Trades
#32451 - 12/23/03 09:52 AM Re: Neutral on back up generator
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
Lot's of code violations but someone else will go into those i'm certain.
Unless he had a double 30 amp breaker he fed his tv with 240 volts.
Top
#32452 - 12/23/03 10:43 AM Re: Neutral on back up generator
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Rob: Could you supply us with any links to an HVAC forum like this one?

Thanks
_________________________
Ryan Jackson,
Salt Lake City
Top
#32453 - 12/23/03 11:00 AM Re: Neutral on back up generator
Rob Offline
Member
Registered: 12/22/03
Posts: 15
Loc: New York
WWW.HVAC-TALK.COM
Good web site for all your HVAC needs.
Commercial and Residential forums.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals