The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Yesterday at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
1 registered (geoff in UK), 205 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#3228 - 08/11/01 11:46 AM 60 volts
Don'tKnowEverythingYet Offline
Member

Registered: 03/18/01
Posts: 22
Loc: Lakewood CA USA
I just spoke on the phone with a homeowner who owns a voltmeter. His clock stopped working overnight. After checking all the usual suspects, he broke out his voltmeter and it read 60 volts where the clock was plugged in. He decided to test the tester and it was reading 120 everywhere else in the house. I didn't know what to tell him; it's usually all or nothing. What would cause this? I've never encountered this situation before. The receptacle is not connected to a wall switch and as far as he could tell(which probably isn't very far) nothing else was connected to that circuit.
Any ideas? Thanks.
BB

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#3229 - 08/11/01 06:19 PM Re: 60 volts
kilowatt1222 Offline
Junior Member

Registered: 11/19/00
Posts: 9
Loc: Bradford,PA
sounds like a lost neutral on the circuit. it could be from the last recept. that feeds the clock cir. I have found broken 'jumpers' on the recepts. that is when the line and load wires are pigtailed on the four scews on the recepts.

Top
#3230 - 08/14/01 01:43 PM Re: 60 volts
Anonymous
Unregistered


I have no good reason to believe that the clock is on a circuit all by itself.

He needs to test the voltage under load and to the EGC.

Top
#3231 - 08/14/01 07:47 PM Re: 60 volts
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Hurry, hurry, hurry to that guys house. I've got a bag full of outlets where the neutral was loose on the outlet. Even where the electrician had spliced the neutral and the rest of the circuit was unaffected. The loose noodle on the outlet itself will heat like a stove element, and it WILL get hot enough to start a fire. Start a collection of your own.

Top