The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (LongRunner, Tjia1981), 178 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#32177 - 12/17/03 10:34 AM Visible power indicator
derater Offline
Member

Registered: 03/30/02
Posts: 182
Have a cust. who wants a way to tell when his power is on at panel.He wants to turn off main to run house via generator when power is out,but know when it comes back on.So connection would have to be before main.Any suggestions?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#32178 - 12/17/03 02:47 PM Re: Visible power indicator
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Use a listed generator tranfer switch. One big enough to do the entire house will be automatic. Any other type will do a portion of the loads so when the remainder come on he will know. Do not rely on him switching the main as the transfer switch.

Top
#32179 - 12/27/03 04:39 AM Re: Visible power indicator
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
I wouldn't recommend the installation of indicators or such devices on the Line-Side of a Main Switch without asking the PoCo first.
Power companies get rather finnicky about things like this, especially where there is a chance that a Generator could back-feed into the Grid.
BTW, I hope that the guy has got a reasonably large generator, you'd be amazed how many people under-estimate the current draw of a few appliances.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#32180 - 12/27/03 05:07 AM Re: Visible power indicator
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
He wants to turn off main to run house via generator when power is out,but know when it comes back on.


This would be a code violation and would be dangerous to utility workers.

Advise the customer strongly to do the right thing as Scott has said.

You should not even consider helping this customer back feed a panel with a generator.

Besides the moral responsibility you have, you will be liable injuries to the utility workers that get blasted by a back feed.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#32181 - 12/27/03 10:09 AM Re: Visible power indicator
Wirenuttt Offline
Member

Registered: 11/10/02
Posts: 267
Loc: Massachusetts
As long as there's a transfer switch involved, maybe your customer possibly lives in an off the beaten track neighborhood where he can't just look out his window and see street lights and the neighbors. So he's probably thinking he doesn't want to let the generator keep running unbeknownst to power being back on. I had a situation like this and simply placed a rated cabinet light into the main panel. Always lit when power was on, off when not.

Top
#32182 - 12/27/03 10:29 AM Re: Visible power indicator
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Wirenutt, I would be interested to know how you attached "a rated cabinet light into the main panel" on the line side of the service disconnect.

230.82 prohibits almost anything from being connected on the line side of the main service disconnect.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#32183 - 12/27/03 03:41 PM Re: Visible power indicator
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
One way that a reasonable level of safety could be acheived, is by the use of 2 inter-locked contactors, so that only 1 can be energised at a time.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#32184 - 12/27/03 05:56 PM Re: Visible power indicator
mvpmaintman Offline
Member

Registered: 09/15/03
Posts: 113
Loc: Manhattan, Kansas, USA
If the guy wants to do it right use a transfer switch that will transfer back when the power is on. Anything else is way too risky.

Top
#32185 - 12/28/03 02:57 AM Re: Visible power indicator
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Hi Trumpy

The rules are pretty strict as far as transfer equipment especially ones that handle the whole service.

 Quote:
702.6 Transfer Equipment.
Transfer equipment shall be suitable for the intended use and designed and installed so as to prevent the inadvertent interconnection of normal and alternate sources of supply in any operation of the transfer equipment.
Transfer equipment and electric power production systems installed to permit operation in parallel with the normal source shall meet the requirements of Article 705.

Transfer equipment, located on the load side of branch circuit protection, shall be permitted to contain supplementary overcurrent protection having an interrupting rating sufficient for the available fault current that the generator can deliver. The supplementary overcurrent protection devices shall be part of a listed transfer equipment.

Transfer equipment shall be required for all standby systems subject to the provisions of this article and for which an electric-utility supply is either the normal or standby source.


 Quote:
230.82 Equipment Connected to the Supply Side of Service Disconnect.
Only the following equipment shall be permitted to be connected to the supply side of the service disconnecting means:

(1) Cable limiters or other current-limiting devices.

(2) Meters, meter sockets, or meter disconnect switches nominally rated not in excess of 600 volts, provided all metal housings and service enclosures are grounded.

(3) Instrument transformers (current and voltage), high-impedance shunts, load management devices, and surge arresters.

(4) Taps used only to supply load management devices, circuits for standby power systems, fire pump equipment, and fire and sprinkler alarms, if provided with service equipment and installed in accordance with requirements for service-entrance conductors.

(5) Solar photovoltaic systems, fuel cell systems, or interconnected electric power production sources.

(6) Control circuits for power-operable service disconnecting means, if suitable overcurrent protection and disconnecting means are provided.

(7) Ground-fault protection systems where installed as part of listed equipment, if suitable overcurrent protection and disconnecting means are provided.


As you can see transfer equipment is not listed, the only way to install transfer equipment that switches the entire service is to get a transfer switch that is also rated/listed as a service disconnect.

I could not put together a couple of contactors or even one contactor that was double throw to make my own transfer switch.

Many panel makers produce a panel with two mains that are mechanically interlocked so only one can be on at a time and are listed as service equipment.

Trumpy I know you know the dangers here but I think many people do not realize that under the right conditions that their little generator can back feed a POCO transformer and produce some high voltages.

Bob

[This message has been edited by iwire (edited 12-28-2003).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#32186 - 12/28/03 06:41 AM Re: Visible power indicator
Wirenuttt Offline
Member

Registered: 11/10/02
Posts: 267
Loc: Massachusetts
IWire;
Real simple, just attach it to any circut breaker as you would a transformer for a door bell. Get a light that's 120 volts but rated at 250 or more.

~Andy

Top