#31958 - 12/11/03 02:24 PM Puck lights and transformers
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 914
Loc: Alpharetta, GA
I've got a little problem. One of my crews prewired a kitchen for puck lights. There are 16 total on 3 switches. They did fine on 2 sets by breaking them up with 3 to 5 on a line, but one line has 6 20 watt lights. the largest stock 12v ac xfmr I can find is 105 watts.

The manufacturer said we could put 2 60 watt xfmr's on 1 line, but this doesn't work. The way they said to do it was just connecting the output leads from 1 xfmr to the other and the lights, this does nothing - the lights don't come on at all. I tried connecting one lead to one puck wire and a lead from the other xfmr to the other puck wire and the remaining 2 leads to each other and the lights do come on, but they rapidly strobe.

Any ideas? Anyone know of a 120-150 watt xfmr for this purpose?
Top
Work Gear for Electricians and the Trades
#31959 - 12/11/03 02:35 PM Re: Puck lights and transformers
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 914
Loc: Alpharetta, GA
I just did a net search and it looks like I should have no problem getting a 150 watt xfmr, but I can't find a small j-box style one locally.
Top
#31960 - 12/11/03 03:25 PM Re: Puck lights and transformers
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
You might want to try Seagull. I believe that they have a 150 and a 300W transformer.
www.seagulllighting.com
Top
#31961 - 12/11/03 03:46 PM Re: Puck lights and transformers
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
We install 300 watt transformers but do not forget this would need 10 awg as 300 watts will be 25 amps or maybe you can add an in-line fuse of 10 or 15 amps depending on your wire size.

The six 20 watt lamps will draw 10 amps.

On the parallel transformer set up, did you reverse the polarity and try it?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#31962 - 12/11/03 05:20 PM Re: Puck lights and transformers
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
I was thinking the same as Bob (iwire), in using a typical dry type power Transformer.

Then you could get sizes of 100 VA, 250 VA, 500 VA and 1,000 VA with Secondary Voltages of 12 VAC, 24 VAC or both!

Definitely need to size conductors per load, and fuse the primary side.
Secondary side could be fused per feeder, or total VA size - but better method would be per feeder.

Scott35

p.s. sorry to post minimal info! reply if more is needed!
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#31963 - 12/11/03 06:32 PM Re: Puck lights and transformers
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Bob,

By the way, what kind of wiring would someone use from the transformer to those hockey puck lights?
Top
#31964 - 12/11/03 07:10 PM Re: Puck lights and transformers
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I do not know Harold, the transformers I have done where for track lighting and some other types of overhead wiring.

We use MC, 10/2 or 8/2 (or 8/3, 8/2 is not always available)

I am fairly certain that getting any of those hidden in a a "puck light" would be a chore.

Hopefully no Wagos used.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#31965 - 12/12/03 04:17 PM Re: Puck lights and transformers
straightedge Offline
Member
Registered: 03/13/02
Posts: 86
Loc: Mesa, AZ
Electric Eagle,

I would suggest that on the set of six puck lights. You use two of those 105 watt stock transformers and split the set up three and three.

I have found that you should only use approximately 80% of the availiable 105 watts. Otherwise the life expectancy on the transformer drastically reduces and you will have a service call.

Tev
Top
#31966 - 12/12/03 05:50 PM Re: Puck lights and transformers
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 914
Loc: Alpharetta, GA
Straightedge, that's the whole problem. It was prewired all on one line and it's too late to change it.

I've found xfmr's online that are exactly what we need, but I can't find one locally. I guess I'm going to have to order one and wait.

Thanks for the advice everyone.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals