#31301 - 11/16/03 10:50 PM Plug Molds instead of receps...
JMichael Offline
Member
Registered: 03/10/02
Posts: 60
Loc: Norwich, NY, USA
Had a strange request today.. A couple renovating there kitchen does not want to see any receps on the walls. Instead they way plug strips / molds on the underside of there cabinets.. Can I do this? I would think as long as they are GFCI protected and spaced as per the code it would be permitted.. Any thoughts?

James
Top
Work Gear for Electricians and the Trades
#31302 - 11/17/03 03:33 AM Re: Plug Molds instead of receps...
Speedy Petey Offline
Member
Registered: 08/29/03
Posts: 173
Loc: Upstate, NY
We've done it several times. Mounted on the wall, just against the bottom edge of the uppers. GFCB's with no problems. You cannot use multi wire circuits though. No way you're going to splice in one of those. One 12/2 is all that's gonna fit.
My only problem is rust over time. Have yet to see one years later to see if it's a concern.
_________________________
Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein
Top
#31303 - 11/17/03 04:15 AM Re: Plug Molds instead of receps...
RickG Offline
Member
Registered: 07/04/01
Posts: 37
Loc: South County, R.I. USA
Isn't there a 18" or 20" maximun height above the countertop that these receptacles can be located?
I have done this several times, I agree, use just one 12-2 romex. Also you may want to keep the plugmold an inch or so from the back wall or edge of cabinet because someday, someone may want plug in an item that has a large male connector or a plug in transformer. If the plugmold is too close to the ajacent wall the transformer or connector may not fit.
Top
#31304 - 11/17/03 02:10 PM Re: Plug Molds instead of receps...
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
I'm partial to mounting the plugmold face down, paying attention to the length of the mounting screws so they don't penetrate the cabinet floor.
_________________________
Al Hildenbrand
Top
#31305 - 11/17/03 02:14 PM Re: Plug Molds instead of receps...
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
I too do this occasionally. It is usually a pain in the rear. Keep this in mind for $$. I try to talk customers out of it. It is a pain to plug things in. You see a cord hanging. Most people have items on the counter they can put in front of a plug to hide them. Another option would be to locate the receptacles just above the countertop horizontally.
Top
#31306 - 11/17/03 04:04 PM Re: Plug Molds instead of receps...
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Speedy,

If you're concerned about rust, there is at least on manufacturer of non-metallic plugstrips.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#31307 - 11/17/03 06:22 PM Re: Plug Molds instead of receps...
master66 Offline
Member
Registered: 04/18/02
Posts: 257
Loc: Masontown, PA, USA
Couldn't you use 2 circuit plug mold and a 2-pole 20A GFCI breaker?

It wouldn't be the cheapest way to go but it would work.
Top
#31308 - 11/20/03 06:52 PM Re: Plug Molds instead of receps...
Active 1 Offline
Member
Registered: 02/22/03
Posts: 687
Loc: Grayslake IL, USA
We were going to do this once. Could not talk the customer out of it.

We put the GFI's in the eating area and load sided off them. Because we pipe everything here and can only use short 3/8 greenfield wips we had to feed them off other boxes that were for the major appliances.

After the granit counter tops were in and the walls were painted they changed their mind and wanted it back in the wall above the counter tops.

As soon as that was chainged they still were not happy. They did not want it the normal hight they wanted them right on top of the backsplash.

Just be worned when the costomer wants a modern home but does not want to see any recepticals you will waste a lot of time.

Tom
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals