#31147 - 11/11/03 06:22 PM sub panel in seperate structure
SCS Offline
Junior Member
Registered: 11/05/03
Posts: 7
Loc: edison NJ
im installing a 100 amp sub in poll barn ,im using PVC and pulling wires .. do i need to pull a ground wire with my feeder conductors ,there will be 2 wires and a nuetral in pipe ,i know i have to drive an additional ground rod at the other building
Top
Work Gear for Electricians and the Trades
#31148 - 11/11/03 06:31 PM Re: sub panel in seperate structure
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
250.32 allows you to use the grounded conductor of the feeder circuit to attach to the grounding electrode of the seperate structure, if you do not pull an equipment grounding conductor.
_________________________
Ryan Jackson,
Salt Lake City
Top
#31149 - 11/11/03 06:32 PM Re: sub panel in seperate structure
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Will there be any other conductive paths to the barn? (ie phone line or metalic water pipe etc...)

If so yes, and you would isolate the neutral from the EGC and the ground rod (GEC)connections.

Even if you are not going to have any other conductive paths right now, it is still the best way to do this. (plan for the future)

Roger
Top
#31150 - 11/11/03 06:36 PM Re: sub panel in seperate structure
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
I should have also pointed to 250.32 as Ryan did.

Specificaly 250.32(B)

Roger
Top
#31151 - 11/11/03 06:39 PM Re: sub panel in seperate structure
SCS Offline
Junior Member
Registered: 11/05/03
Posts: 7
Loc: edison NJ
so i should add the EGC
im running 1/0 copper what size should the EGC be ??
Top
#31152 - 11/11/03 06:41 PM Re: sub panel in seperate structure
SCS Offline
Junior Member
Registered: 11/05/03
Posts: 7
Loc: edison NJ
did i say thank you for the fast reply ??
Top
#31153 - 11/11/03 06:45 PM Re: sub panel in seperate structure
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Your welcome.

If you decide to use an equipment ground, you cannot use the nuetral for attachment to the grounding electrode.

If you do not pull an equipment ground you may use the nuetral for attachment to the grounding elctrode.

Dealer's choice!
_________________________
Ryan Jackson,
Salt Lake City
Top
#31154 - 11/11/03 06:48 PM Re: sub panel in seperate structure
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
I'm sorry i missed half of your question. REmember that EGC's are driven by the size of the breaker, not the size of the conductor. 250.122 tells me that #8 is fine.
_________________________
Ryan Jackson,
Salt Lake City
Top
#31155 - 11/11/03 06:51 PM Re: sub panel in seperate structure
SCS Offline
Junior Member
Registered: 11/05/03
Posts: 7
Loc: edison NJ
thanks guys
Top
#31156 - 11/11/03 07:03 PM Re: sub panel in seperate structure
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
SCS, Welcome to the forum.

I personaly would install the EGC.

Roger
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals