The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
40 minutes 47 seconds ago
Safety at heights?
by gfretwell
Today at 07:16 PM
failed home inspection.
by gfretwell
Today at 07:03 PM
Webmaster > Admin
by Admin
Today at 05:49 PM
Old Bath Fan
by gfretwell
Today at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
1 registered (Admin), 0 Guests and 184 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#30928 - 11/03/03 04:42 AM Voltage leak
tonyc Offline
Member

Registered: 09/27/02
Posts: 18
Loc: Chesapeake, Va
Checked out a newly wired pre fabbed house.

When light switches are turned off found about 30 volts still on the line has anyone seen this? This switch is supposed to be completey open, can't be a bad ground or neutral,switch is supposed to be open.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#30929 - 11/03/03 08:29 AM Re: Voltage leak
bigrockk Offline
Member

Registered: 01/25/03
Posts: 175
Loc: Middle of Canada
Hello Tony
Try checking the circuit when there is a "load" applied,(ie a light bulb)my guess is you will find that your 30 volts has dropped off to "0".
It is possible that high humidity is causing a small leakage across the switch.
Did you find the leakage on more than one circuit? If so suspect the humidity,if it is only one circuit suspect the switch.
Good luck

Top
#30930 - 11/03/03 10:10 AM Re: Voltage leak
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Tony,
Are you using a digital meter? Is the hot and the switch leg in the same run of NM cable? If so the reading is normal. Is there a load connected to the switch?
Don
_________________________
Don(resqcapt19)

Top