The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#30843 - 10/29/03 07:22 AM Oil Change Facility
mvrandazzo Offline
Member

Registered: 05/13/02
Posts: 105
I receintly did some work in a Oil Change facility. I noticed in the pit that the wiring method was EMT and some rigid for physical protection. Is this supposed to be a classified locaiton?

Blessings, Mark

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#30844 - 10/29/03 08:11 AM Re: Oil Change Facility
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The pit is normally unclassified based on the use of ventilation. See 511.3(B)(3) which sends you to Table 514.3(B)(1).