#30843 - 10/29/03 07:22 AM Oil Change Facility
mvrandazzo Offline
Member
Registered: 05/13/02
Posts: 110
I receintly did some work in a Oil Change facility. I noticed in the pit that the wiring method was EMT and some rigid for physical protection. Is this supposed to be a classified locaiton?

Blessings, Mark
Top
Work Gear for Electricians and the Trades
#30844 - 10/29/03 08:11 AM Re: Oil Change Facility
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
The pit is normally unclassified based on the use of ventilation. See 511.3(B)(3) which sends you to Table 514.3(B)(1).
don
_________________________
Don(resqcapt19)