The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#30760 - 10/27/03 10:57 AM splicing grounding electrode conductor
donles Offline
Member

Registered: 04/28/01
Posts: 82
Loc: Pennsylvania
Does any one splice or tap to the GEC?
What do you use? I'm upgrading a duplex with 100 amp panels side by side in the basement.
Rather than run two #6 solid cu from each panel to the ground rods outside, I'd like to run from one panel to the rods. Then run #6 from the 2'nd panel and tap onto the 1'st panel's GEC using irreversible compression-type connectors. I believe this is permitted by NEC 250.64 (C) and (D).

I've checked with 2 supply houses and they evidently do not carry a compression tool or the connectors. Anyone have experience with this?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#30761 - 10/27/03 12:09 PM Re: splicing grounding electrode conductor
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Donles,
Burndy, Thomas & Betts, and Anderson are the ones that make the tools and materials off the top of my head. All of these can be found by a simple web search.

If you quit that solid habit, you can use a Cadweld, made by erico www.erico.com
These are reusable for a long time, and do not degrade like crimps or split bolts.

Top
#30762 - 10/27/03 01:27 PM Re: splicing grounding electrode conductor
donles Offline
Member

Registered: 04/28/01
Posts: 82
Loc: Pennsylvania
What is the ballpark cost for Cadweld?

I've found the cost of the T&B tools to be prohibitive for my infrequent use. Although I did see a Penn-Union tool on ebay for what is probably alot less than retail. Minimum bid $99 for a TDM-250 and the auction was winding down.

Top
#30763 - 10/27/03 02:01 PM Re: splicing grounding electrode conductor
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
I normally use a split bolt for this.

Top
#30764 - 10/27/03 02:26 PM Re: splicing grounding electrode conductor
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Split bolts are not irreversible. Perhaps you're thinking of an equipment grounding conductor and not a grounding electrode conductor?
_________________________
Ryan Jackson,
Salt Lake City

Top
#30765 - 10/27/03 02:37 PM Re: splicing grounding electrode conductor
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
If you do a search on this site for cad welds you will find a thread that talks about one shot disposable cad welds for $5.00 I have not used them but it sounds like a great deal.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#30766 - 10/27/03 03:40 PM Re: splicing grounding electrode conductor
donles Offline
Member

Registered: 04/28/01
Posts: 82
Loc: Pennsylvania
I looked at Erico's site for the one-shot, inexpensive cadweld splices. Their site isn't the most user friendly. I did come across mold # PG11L for #4 solid to #4 solid taps but no details. I'll have to call suppliers tomorrow.
Thanks.

Top
#30767 - 10/27/03 04:10 PM Re: splicing grounding electrode conductor
eprice Offline
Member

Registered: 08/07/03
Posts: 64
Loc: North Logan, Utah, USA
Ryan,

Couldn't 250.64(D) be used here, and wouldn't that allow the use of something like a split bolt to make a tap to a second enclosure as long as the GEC to the first enclosure meets 250.64(C) and is not spliced where the tap joins?

Top
#30768 - 10/27/03 04:24 PM Re: splicing grounding electrode conductor
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
EPRICE: Thanks! I got so caught up the topic starter's question of how to do it irreversibly that I didn't look at the code. Good catch.

Scott: Sorry!
_________________________
Ryan Jackson,
Salt Lake City

Top
#30769 - 10/27/03 05:20 PM Re: splicing grounding electrode conductor
donles Offline
Member

Registered: 04/28/01
Posts: 82
Loc: Pennsylvania
Care to expand on that a little?
Meanwhile, I'll consult the code.

Top