#30754 - 10/27/03 10:24 AM Separately Derived System
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
In a large industrial facility where you have transformers through-out the buildings, is each transformer considered separately derived? These would be a typical 45-100 KVA, with 480 primary and 110/208 secondary. The only place you bond the nuetral and ground would be at the main service. All panels after that, the nuetal bars and equipment grounds would be separate, right? An engineer wanted UPS panels treated like Main panels, and I was telling him that you have to treat them like sub panels. Just because a UPS feeds a panel, it's not the same as a separately derived system. It would be great if some one could clarify this. These transformers would all be in the same building. Thanks
Top
Work Gear for Electricians and the Trades
#30755 - 10/27/03 10:38 AM Re: Separately Derived System
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
The transformers are SDS and require a neutral to ground bond on the secondary side. UPS systems are, in general, also SDS and require neutral to ground bonds on the load side.
_________________________
Don(resqcapt19)
Top
#30756 - 10/27/03 10:43 AM Re: Separately Derived System
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Are there cases in the U.S. where with a wye-wye xfmr you might ground the secondary neutral by connecting it to the primary neutral, rather than direct to ground?
Top
#30757 - 10/27/03 12:18 PM Re: Separately Derived System
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
Paul,
What is it about YOU and sticky questions???
Danged Brit troublemaker!!!!!!

Long contentious argument about primary/secondary applications. Yes, there are those types applications though most inside wireman never get into them.

Wye/Wye tend to get connected in the transformer and yes, they are the same as bolted together in these apps. Some engineers claim that the procedure is proper, and I have been involved in curing the subsequent problems by separation.

Regardless the code (seems) is clear that it is an SDS, and it appears grounded properly even though both ground to case. This, of course, renders so much current flow between the two as to render your suppression technique nearly useless, and your coordination practically impossible.

The correction is to isolate in the transformer (whichs SEEMS to be a violation of the NESC) and bond the secondary ONLY at the building served.

This flies in the face of most POCO manuals and unless you have the authority (it was nice that when I found this problem I was in that position) it is difficult to isolate the two and still have a meter in your installation.

Again, sticky question @@#$%$%^^@$ Redcoat.
Top
#30758 - 10/27/03 04:54 PM Re: Separately Derived System
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
This topic comes up so often, that it might be a benefit for all of us if I compile as much information possible, plus draw some Schematics for several Scenarios, then post in the Technical Reference area.

Any information that memebrs can supply to me will be greatly appreciated!

I am looking for anything regarding the topic of SDS's; Codes, Best for UPS, anything at all!

Will use information that has been successfully debunked in said presentation post.

Send information to me via E-Mail by using the E-Mail icon at top of this message.
(FYI: address is adst at pacbell dot net)

Please begin the message's subject with "Per ECN Topic of SDS", and include your name/user name. (p.s. don't "Quote" the text as I have done in the above example)

I ask you to do this so your messages get filtered into a "Good Place"

TIA!!!

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#30759 - 10/28/03 09:44 AM Re: Separately Derived System
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
George,
It's all of you Colonials causing the problems! Nothing but trouble ever since that little disagreement over some tea...
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals