The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 236 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#30535 - 10/22/03 07:18 AM Fiberglass piping in chemical atmospheres
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
What are the recommended procedures for grounding and bonding fiberglass piping in chemical atmospheres?

Are there any available documents, or publications that can be used by operator's?
_________________________
Joe Tedesco, NEC Consultant

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#30536 - 10/22/03 08:43 AM Re: Fiberglass piping in chemical atmospheres
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Joe,

Are you referring to minimizing static electricity?

Top
#30537 - 10/22/03 08:54 AM Re: Fiberglass piping in chemical atmospheres
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Redsy:

Yes, that's one the reasons for this question.

The facility uses various highly flammable fluids, such as acetone, methanol, and ethanol.
_________________________
Joe Tedesco, NEC Consultant

Top
#30538 - 10/22/03 10:12 AM Re: Fiberglass piping in chemical atmospheres
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Joe,
I don't understand how nonconductive piping can be bonded or grounded?
Don
_________________________
Don(resqcapt19)

Top
#30539 - 10/22/03 11:02 AM Re: Fiberglass piping in chemical atmospheres
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Don,
In an explosive atmosphere you MUST bond your plastics because of the static, you create one VERY big problem if you don't

Joe, I always had to rely on the manufactures info for this. There is so little in the code, and even IEEE documents that you had to rely on the UL ratings and user guides.

NFPA 77 can be very instructive in this case as well.

Top
#30540 - 10/22/03 01:27 PM Re: Fiberglass piping in chemical atmospheres
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Geroge,
I know that sometimes a metallic path is provided to discharge static along a nonmetallic transfer system, but I don't consider that bonding or grounding of the nonconductive piping system. You can not make an effective grounding or bonding connection to a nonconductive object.
Don
_________________________
Don(resqcapt19)

Top
#30541 - 10/22/03 02:42 PM Re: Fiberglass piping in chemical atmospheres
walrus Offline
Member

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
Wouldn't the static buildup inside the piping, where the fluid flow is??? So wouldn't it follow that some type of wire inside the piping, possibly bonded to the core of the pipe. I've seen and installed lots of fiberglass piping. Never seen a static strap except on plastic(HDPE) piping that connected to a brass fitting at a termination

Top
#30542 - 10/22/03 02:51 PM Re: Fiberglass piping in chemical atmospheres
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
I found a position paper from the "Fiberglass Pipe Institute" that verifies the hazards and supports some of the positive comments made here.

 Quote:
Nonmetallic fiberglass pipe and fittings are available with a grounding wire entrained in the resin and meets MIL-P-29206A for jet fuels and petroleum liquids.
_________________________
Joe Tedesco, NEC Consultant

Top
#30543 - 10/22/03 06:56 PM Re: Fiberglass piping in chemical atmospheres
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Joe,
That makes a lot more sense. Now we are bonding or grounding a conductive object, not just a nonconductive pipe. There is some information in the IEEE Green Book that says a bonding/grounding path with a resistance of up to 1,000,000 ohms is sufficient to prevent the build up of static charges.
Don
_________________________
Don(resqcapt19)

Top
#30544 - 10/23/03 03:51 AM Re: Fiberglass piping in chemical atmospheres
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Don,
There are many instances where a simple piece of PVC can harbor sufficient static to create an explosive atmosphere, especially along the inside wall of the pipe.

In these cases, you can also ty-wrap a simple piece of #12 alongside the outer edge to dissipate your charge. As long as it is continuous, the ohmic value can be as great as 1 meg with no harm to the value of the ground.

What !!! never made a rubber battery?

Top