The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 238 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#30415 - 10/17/03 06:39 PM Interesting 3 phase results
Clyde Offline
Member

Registered: 10/17/03
Posts: 31
Loc: Leamington
I had something new happen to me last night, I've asked two other electricians and they don't have an answer for me either. I had a 3 phase, 4 wire 600 volt splitter, and I needed to power a 347 volt light, while I changed a single phase 120/240 volt x-former to a three phase 120/208. When I turned on the disconnect for the light, the light didn't come on. I checked the voltage and found 120 volts on the phase I was hooked to, I found 780 volts on another phase and over 800 volts on the next phase. I tried to hook the light to a different phase and had the smae results. With no lights hooked up, everything is normal. Has anyone seen this before.
Thanks.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#30416 - 10/17/03 08:38 PM Re: Interesting 3 phase results
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
It sounds like a loose connection somewhere. Possibly in the splitter or even all the way back to the poco's xfmr. You said 4 wire, so it could be the neutral, I've seen similar results with a loose neutral before.

Top
#30417 - 10/17/03 09:03 PM Re: Interesting 3 phase results
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
I agree.
Sounds like you are reading the resultant voltage of Capacitive Coupling (if you are reading L-G and getting the wierd readings as stated).

Make sure the Common Grounded Conductor (AKA "neutral") is connected properly between source and load(s).
Also make sure the Equipment Grounding Conductor is connected properly between source and load(s).

Sounds like you have both - an open Noodle and an open Eq. Grounding Conductor, only the EGC is physically connected to earth ground somewhere, but not connected to the source's Grounded Conductor.

Just guessing...

Let us know the outcome!

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#30418 - 10/18/03 04:16 PM Re: Interesting 3 phase results
Pinemarten Offline
Member

Registered: 08/23/03
Posts: 122
Loc: Edmonton, AB, Canada
Another thought or two....
Are the ballast taps marked correctly, is the ballast capacitor hooked up correctly, does the voltage change when the lamp is in or out of the socket?
I think there are drawings in the technical reference section.

Top
#30419 - 10/18/03 06:09 PM Re: Interesting 3 phase results
Clyde Offline
Member

Registered: 10/17/03
Posts: 31
Loc: Leamington
I did check the neutral today and did find a fair amount of resistance between the neutral buss and ground. Perhaps this is the problem.

I also found out that the building is currantly fed with an open delta configuration due to a destroyed transformer. That shouldn't cause a problem though.

I appreciate your responses guys.

Top
#30420 - 10/23/03 02:01 PM Re: Interesting 3 phase results
Clyde Offline
Member

Registered: 10/17/03
Posts: 31
Loc: Leamington
After a little more research, I've discovered that the open delta configuration is the problem.

When an open delta configuration is used, only three wires are available from the transformers. Leaving you without a center-tapped neutral. I'm still learning every day.

Thanks.