ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
Anyone hiring inspectors?
by gfretwell. 03/27/17 01:36 AM
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,551 Are you busy
166,289 Re: Forum
160,676 Need opinion
Who's Online Now
0 registered members (), 43 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#30407 - 10/17/03 08:49 PM Blackout of 2003  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
I saw a presentation last night put on by our local POCO, (LIPA) on the chain of events leading up to the Blackout on Long Island (NY) and the challenges faced in getting everything back online. The speaker was the person in charge of keeping all of the High Voltage lines in operation. He went on to talk about what he says was the worst (and most educational) 26 hrs of his life.

I don't know a lot about this stuff, but what he said sounded logical to me and some of the problems mentioned in getting things back on line also made sense and I think we may take these guys for granted a bit much sometimes. It sounds like a whole lot more than just flipping switches back on. My hat's off to anyone involved in bringing things back that might be reading this.

[Linked Image] [Linked Image]
Bill


Work Gear for Electricians and the Trades

#30408 - 10/18/03 07:58 PM Re: Blackout of 2003  
Pinemarten  Offline
Member
Joined: Aug 2003
Posts: 123
Edmonton, AB, Canada
I used to work at a plant that had three services all pulling just under a gigawatt (1,000,000,000w). The POCO had an automatic cut-out if it went over, which I remember happening at least once. This was caused by large shorts on our end.

-production staff would go to 'general coffee', and the emergency generator would hopefully start

-everyone would shut up on the radio, except the electricians

-the electrical super or plant engineer would assign tasks to 3-14 electricians, depending on the time of day (24/7 production, $20,000/min downtime)

-we would then start isolating sections of the plant

-the power would return automatically

Start panicking, but remain calm and follow instructions.

-we had to bring everything back online in an order that both avoided inrush trips, as well as the most cost effective order for production

-the short would usually show up at this time, and trip us out again.

Remember which breaker you were turning on when the lights went out the second time.

Power failures from outside would have a similar procedure.
The plant has been expanding since construction in the '60s-'70s, and the staff keeps tuning the procedure. My contribution was putting an emergency light in the electrical shop.


#30409 - 10/18/03 08:38 PM Re: Blackout of 2003  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
Some of the problems discussed had to do with getting the different type of generators restarted, Steamline ruptures, purging and re-energizing some liquid-filled power lines (?) stabilizing frequency as things were started up and loads were added.

It seemed like they had to be very careful about what they did until they were re-connected to the main grids, because unbalances could easily cause frequency change and automatic load-shedding or over/under frequency relays to drop out and shut things down again.

He used an analogy to describe how important the stability of being connected to the main grid that I don't know how accurate it is but I thought was great. It was something like this:

Picture the load as being a child jumping up and down on a bed. Picture the generating plants across the country all connected together as a 100 pound weight. When the child jumps up and down on the bed it doesn't have much effect on the weight. Now picture unconnected generating plants as 100 one pound weights. Each time the child jumps on the bed some will fall off until all are gone.

Bill


#30410 - 10/18/03 09:03 PM Re: Blackout of 2003  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Bill, That must have been a fascinating meeting.

I have been curious about the ins and outs of the cause and restoration of that power failure.

The news reports are not technical or half the time even believable.

Bob




[This message has been edited by iwire (edited 10-18-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#30411 - 10/18/03 10:33 PM Re: Blackout of 2003  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
There is a lot of information from the House Energy Subcommittee Hearing . You can read about 650 pages of phone transcripts from the Midwest ISO control center.
don


Don(resqcapt19)

#30412 - 10/19/03 08:13 AM Re: Blackout of 2003  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
Your getting warmer Don... [Linked Image]

Did you guys also Catch Petaki, Bloomberg & Bush (among others) rehtoric ?

anything to do with energy is going to be prostituted...we mere mortals will simply be along for the ride...


#30413 - 10/19/03 02:30 PM Re: Blackout of 2003  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
Bob,

Yes, it was an interesting meeting. Things like this are a benefit of being a member of a local organization. We have a chance to interface with them (POCO) at every meeting.

Bill


#30414 - 11/20/03 01:44 AM Re: Blackout of 2003  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
On the 14-AUG outage...
http://www.energy.gov/engine/conten...DE=DOEHOME&TT_CODE=SPOTLIGHTDOCUMENT
http://www.nerc.com/~filez/blackout.html



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,428
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7936 MB (Peak: 0.9508 MB) Zlib enabled. Server Time: 2017-03-27 08:32:12 UTC