#30171 - 10/06/03 07:33 PM Why don't they make a true AFCI & GFCI in one breaker?
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Or maybe they do and I just don't know it, but I could've used one today.

We upgraded the service on a 1972 house from 150 amp to 200 amp with a larger panel to allow for a large addition the homeowner is planning. While labeling the new panel, we discovered that the entire upstairs - 4 bedrooms, 2 bathrooms, the attic, hall, and a whole house fan were on one 15 amp circuit. This circuit was on a GFCI breaker, I guess to protect the bathroom outlets, but we had to replace it with an AFCI to comply with 210.12(B). If AFCI's were also GFCI's, then that would be the end of it, but we now have to change the bathroom outlets to GFCI's. I'm actually going to try to sell the homeowner an upgrade of the bath outlets to a 20 amp circuit and splitting the rest of the circuit into 3 circuits, but that's beside the point.

If an AFCI can detect a ground fault, why don't they make them compliant with AFCI and GFCi rules?
Top
Work Gear for Electricians and the Trades
#30172 - 10/06/03 07:38 PM Re: Why don't they make a true AFCI & GFCI in one breaker?
caselec Offline
Member
Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
EE

Cutler-Hammer does make combination AFCI/GFCI breakers. If you need a part number I will look it up for you. I don't know if any of the other manufactures plan on offering a combination device. I read on one of the forums that Square D was going to offer one but I haven't seen it yet.

Curt
_________________________
Curt Swartz
Top
#30173 - 10/07/03 02:00 PM Re: Why don't they make a true AFCI & GFCI in one breaker?
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Listing of AFCI 'devices' has 6 categories in the UL White Book.
The 'combo' unit is not an AFCI/GFCI unit. What is technically a combo unit is: The unit will protect the branch circuit, AND the cord plugged into the receptacle outlet.

Square D has a 'combo' unit coming out in early 2004. Again combo does not mean AFCI/GFCI.

All manufacturers of AFCI breakers produce their product with class B level GFCI in the same unit as the AFCI.

In studies performed recently, the reason for AFCI breakers tripping 83% of the time is because of faulty wiring conditions tripping the GFCI portion of the AFCI breaker (grounded conductor to equipment grounding conductor connections).

Pierre


[This message has been edited by PCBelarge (edited 10-07-2003).]
_________________________
Pierre Belarge
Top
#30174 - 10/07/03 06:29 PM Re: Why don't they make a true AFCI & GFCI in one breaker?
caselec Offline
Member
Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Pierre

I guess I used the wrong terminology when I called it a combo unit. Cutler-Hammer makes AFCI breakers that also have class A GFCI protection.

The part numbers are:
BR115AFGF
BR120AFGF
CH115AFGF
CH120AFGF

Curt
_________________________
Curt Swartz
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
Today at 02:34 PM
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades