The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 223 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#30015 - 09/28/03 09:26 PM UF in pipe
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
I saw a job where the customer ran UF in PVC pipe underground. Now I know your not supposed to run NM but what about UF? Is it legal? I would think it would be.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#30016 - 09/28/03 10:41 PM Re: UF in pipe
stamcon Offline
Member

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
The 99NEC permits UF and NM cables to be run in pipe(NM can't be in a "wet" location). 300-5(c) requires cables installed under buildings to be in a raceway. 300-5(d) requires direct buried conductors and cables emerging from the ground to be in an enclosure or raceway from the minimum cover distance to at least 8' above finished grade.

Top
#30017 - 09/30/03 05:31 PM Re: UF in pipe
Speedy Petey Offline
Member

Registered: 08/29/03
Posts: 175
Loc: Upstate, NY
What about an assembly being in a raceway?
In this case UF and NM are basically the same thing, no?
A sleeve up the side of a structure I can see but not a complete conduit.
_________________________
Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

Top
#30018 - 10/01/03 01:40 AM Re: UF in pipe
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Using PVC to protect NM cable from physical damage is spelled out in 334.15(B)

And 340.10(4) tells us that the rules of 334 will apply to UF cable.

Also 300.5(D)(1) requires direct buried cables and conductors emerging from grade are to be protected from damage.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top