The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 102 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#29552 - 09/19/03 03:40 AM Gasoline shutdowns
walrus Offline
Member

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
I work in a lot of locations in which the fire suppression folks have a shutdown that is supposed to stop the flow of gas when the fire suppression pull box is pulled. The way they do it is, interupt the neutral going to the coils of the relays for the pump motors. They use a normally closed relay that opens when the pull station is pulled. It works but is it right????

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#29553 - 09/19/03 03:55 AM Re: Gasoline shutdowns
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
hmmm, maybe it's just my personal experience walrus, but i've been used to contactor controlled subpanels in gas stations.....

Top
#29554 - 09/19/03 04:30 AM Re: Gasoline shutdowns
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
This is the way many factory wired motor starters work with relationship to the overload relays.
On an ungrounded control circuit this might be OK, but on a control circuit using a grounded conductor I don't like it.
There is the potential for a ground fault between the coil(s) and the contact that is used to interrupt them to render the shutoff (or tripped O/L) totally inoperable.
Under normal operation, this ground fault could go undetected indefinitely. The first sign could be that the shutoff doesn't work when called upon to do its (important) job.
This situation could be compounded by multiple starters/relays wired in conjunction with each other...S

Top
#29555 - 09/19/03 01:08 PM Re: Gasoline shutdowns
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
That type of installation appears to be a violation of 430.73.
Don
_________________________
Don(resqcapt19)

Top
#29556 - 09/19/03 03:44 PM Re: Gasoline shutdowns
walrus Offline
Member

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
I always thought that switching the neutral like that wasn't right but wasn't 100% sure why.


I have some contactor controlled installs but few and far between. The reason they shut down the neutral is because there is several relays controlling several pumps but only one neutral to all relays. Easy?....

I'm involved in a location that has no shutdowns and they want to put one in. No chance they spring for the money to put in a contactor,although I'm thinking shunt trip?? and a contactor might be cheaper.
Any other suggestions???

Top
#29557 - 09/19/03 10:02 PM Re: Gasoline shutdowns
wa2ise Offline
Member

Registered: 11/29/02
Posts: 771
Loc: Oradell NJ USA
This can only work if all the pumps are fed by the same voltage and phase. If the pumps are on 2 or three phases (each pump using only one phase), and you break the neutral, the pumps would still have voltage across them. Only if each pump draws the same current would they split up the supply voltages evenly. In any event you wouldn't get shutdown.

If everything is fed by one voltage/phase source, then you could put that contactor on the supply wire, and leave the neutral alone.