The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by Texas_Ranger
24 minutes 10 seconds ago
100% breakers?
by Texas_Ranger
28 minutes 26 seconds ago
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 10
Trumpy 8
Who's Online
2 registered (LongRunner, Texas_Ranger), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#29307 - 09/13/03 03:58 PM ampacity
Eandrew Offline
Member

Registered: 05/24/02
Posts: 69
Loc: seattle, wa, usa
I was wondering why, when the definition of ampacity is " the continuous current that a conductor can carry without exceeding its temperature rating (as listed in 310.16) do you still have to increase that ampacity 125% for a continuous load. Is the word "continuous" in the definition of ampacity not the same a "continuous " in continuous load?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#29308 - 09/20/03 09:50 AM Re: ampacity
triple Offline
Member

Registered: 04/01/02
Posts: 182
Loc: Wisconsin
I could be wrong (often am) but I thought the 125% was primarily factored in for the OCP. Most OCPs are not rated for continuous use at 100%. As far as I know, as long as the rules for all other variables (such as #CCC, amb. temp, termination rating, OCP, etc.) are adhered to, conductors CAN be used at 100% of their capacity for an indefinite period of time. Am I wrong again?

Top
#29309 - 09/20/03 10:37 AM Re: ampacity
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Erik, look here. http://electrical-contractor.net/ubb/Forum2/HTML/000583.html

You'll find this familiar.

Roger

Top
#29310 - 09/22/03 01:26 PM Re: ampacity
triple Offline
Member

Registered: 04/01/02
Posts: 182
Loc: Wisconsin
How do ya like that...I was right this time. It was bound to happen sooner or later.

Top
#29311 - 09/22/03 04:51 PM Re: ampacity
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Triple, don't cut yoursef short.

Roger