#28945 - 09/04/03 10:48 PM 400 amp panel upgrade
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
A customer has a 3500 sq ft home and wants to upgrade his 200 amp 1Ph panel because it is full and he wants to add a 240v 50a spa, a 240v 20a waterfall and a 500 sq ft guest house with elec heat, kitchen etc. If I do this the power co will have to pull in new feeders from the transformer and I'll have to use 2 - 200 amp panels. One main 200 amp panel feeding another 200 amp load center. (As far as I know they don't make a all-in one 400 amp panel). These are outdoor panels which are mostly used here in AZ. Cost is around $1000 just for the parts.
Option 2: is possibly adding a 100 amp sub panel off the exhisting 200 amp panel, (having to make room for the 100a feeder breaker), this would be less expensive.
I'm going to amp clamp the load, also will figure the total load service calculation from the back of the code book.
Any suggestions, comments, or ideas on this?
Thanks,
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Work Gear for Electricians and the Trades
#28946 - 09/05/03 03:58 AM Re: 400 amp panel upgrade
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Have you calculated for additional load in existing dwellings, per 220.31?
It should be less stringent, and you may be able to squeeze in on your existing service.
Top
#28947 - 09/05/03 08:00 AM Re: 400 amp panel upgrade
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
Have not figured load calc yet but will include that.
thanks,
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#28948 - 09/05/03 08:27 AM Re: 400 amp panel upgrade
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
Aldav

All of the big manufactures (GE, Square D, Cutler-Hammer, Siemens, Etc.) make 400 amp combination service entrance devices. You can get them with a single 400 amp breaker feeding the internal 40 circuit loadcenter or with 2-200 amp breakers, 1 feeding the internal loadcenter and the second to feed a remote panel. Square D only make one with the 2-200 amp breakers but I know GE and Cutler-Hammer makes both styles. If you need some part numbers let me know.

Curt
_________________________
Curt Swartz
Top
#28949 - 09/05/03 02:59 PM Re: 400 amp panel upgrade
targetshootr Offline
Member
Registered: 05/02/03
Posts: 55
Loc: nc
what type heat does the main house have. that is my rule of thumb guide to service sizes, along with sq footage. if they have gas, i'd probably use the existing service. if they have heat pumps, they're probably stretched thin already. either way heres a real time saver for figuring the load:
http://www.vickrey-s.com/SFDLoadCalc.asp
Top
#28950 - 09/05/03 03:04 PM Re: 400 amp panel upgrade
targetshootr Offline
Member
Registered: 05/02/03
Posts: 55
Loc: nc
oh, if i were to upgrade to 300 or 400amp, i'd use a ct cabinet, or the newer 300amp meter base, and set the 200amp panels to each side. probably save a bundle compared to a 400 amp switch.
Top
#28951 - 09/05/03 07:58 PM Re: 400 amp panel upgrade
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
He has 2 electric heat pumps with 2 air handlers, but the water heater is gas.
Are those outdoor all-in-one 400a panels?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#28952 - 09/05/03 08:19 PM Re: 400 amp panel upgrade
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
All of the 400 amp Combination Service Entrance Devices are NEMA 3R.

Here is a link to Cutler-Hammer's Combination Service Entrance devices. Look at pages 22-26 of the PDF file. http://www.cutler-hammer.eaton.com/unsecure/cms1/TD31F01TE_72DPI.PDF
_________________________
Curt Swartz
Top
#28953 - 09/06/03 11:53 AM Re: 400 amp panel upgrade
straightedge Offline
Member
Registered: 03/13/02
Posts: 86
Loc: Mesa, AZ
Aldav,

If you go to the "Home Depot Pro", at the NW corner of Thomas and 32nd street.

In there they have 400amp all-in-ones for Square D and Cuttler Hammer.

That store is made for contractors like yourself.

About $800.00 each.

Like one of the posts said. It has two 200amp breakers. One feeds the 40 space panel built inside and the other 200-amp breaker will feed a remote panel.

The only thing that sucks is that the existing Underground PVC pipe, comming from the transformer, will be to small for SRP to pull in bigger feeders. In order to run a bigger PVC conduit, say 3" or 4", you usually have to saw cut the driveway.

I usually try to make the existing 200-amp panel work. Install a 100-amp sub panel like you said.

Good luck.

Tev
Top
#28954 - 09/06/03 07:23 PM Re: 400 amp panel upgrade
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
I checked with SRP and they did say they could pull in new 4/0 feeders for it but think I'll try to go with the 100 sub panel like you said instead.
Thanks,
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Page 1 of 4 1 2 3 4 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals