The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#28269 - 08/15/03 09:35 AM AIC ratings
rmiell Offline
Member

Registered: 11/09/00
Posts: 261
Loc: La Junta, Co. USA
If you have a panelboard rated 22k AIC, and you install a breaker rated only 10k AIC, and assuming no series combo ratings, is the complete setup rated 10k or 22k?

Where is this addressed in the NEC?

Thanks

Rick Miell

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#28270 - 08/15/03 10:31 AM Re: AIC ratings
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
If the available current at the line side of the breaker exceeds 10k, you can't install that breaker. See 110.9. I guess you would have to say that the set-up is only good for the 10k after you install the 10k breaker. It doesn't really change the rating of the panel or the other breakers, but prohibits the use of the panel with the 10k breaker on a system where the available fault current exceeds 10k.
Don
_________________________
Don(resqcapt19)

Top
#28271 - 08/15/03 02:10 PM Re: AIC ratings
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Don,
Would the NEC allow a breaker rated lower than the prospective fault current if there is a properly rated OCPD upstream?

We commonly use domestic breakers rated 6000A AIC here on supplies capable of delivering a much higher current. The higher AIC rating of the main cartridge fuse is considered adequate protection against a dead short.

Top
#28272 - 08/15/03 09:05 PM Re: AIC ratings
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Paul,
If it is a listed and tested "series rated" system, a lower rated breaker may be used. This system cannot be calculated based on let through curves or any other type of calculation. It must be tested by a testing lab and listed.
Don
_________________________
Don(resqcapt19)

Top
#28273 - 08/16/03 01:44 AM Re: AIC ratings
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Ah, so only if the actual series combination is listed for such use then. Thanks.