#2805 - 07/25/01 07:05 PM Service
evan Offline
Junior Member
Registered: 07/25/01
Posts: 1
Loc: Fancy Farm KY
I noticed in the code that a service head had do be atleast three feet from a window.

How far does a meter base have to be from a window.
_________________________
evan elder
Top
Work Gear for Electricians and the Trades
#2806 - 07/26/01 04:18 AM Re: Service
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Evan,

Welcome!
Our local utility (LI, NY) requires that it not be under a window. Other than that I don't know of any other rules on the subject. Maybe you have a local requirement.

Bill
Top
#2807 - 07/27/01 05:12 AM Re: Service
cinkerf Offline
Member
Registered: 12/03/00
Posts: 84
Loc: Pittsburgh, Pennsysvania. ...
Evan,

Our local power company provides a small code book of their own. I couldn't find a rule concerning placement near window. In the past I've installed meter enclosures less than three feet from window and had no problem with it passing elec. inspection. Mounting height must be five to six feet.

Frank
Top
#2808 - 07/27/01 05:42 AM Re: Service
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Evan,

Just as a comparison to Frank's comments, We are allowed a height of 3 to 6 ft. So, you see everywhere can be different. It's not a code requirement.

Bill
Top
#2809 - 07/27/01 08:39 AM Re: Service
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
My take on it..

I believe this clearance issue is rooted in 230-9, which requires claerance for open conductors without an overall jacket. The service drop, which is spliced at the service head is typically open conductors, and therefore subject to the clearance requirements. The service entrance conductors, which may be jacketed SE Cable would not be subject ot the clearances due to the overall jacket, and may pass closer to windows etc.
This probably would apply to the meter socket as well, unless local or utility rules prohibit it.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals