#28002 - 08/07/03 01:01 PM Floor Outlets
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
I have installed a flat cable under a carpet in a commercial building years ago (expensive I believe). Do they make a cable to install in a residential home under the carpet to add a floor outlet? Is there something better than chisling out the cement and laying pvc?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Work Gear for Electricians and the Trades
#28003 - 08/07/03 02:18 PM Re: Floor Outlets
SvenNYC Offline
Member
Registered: 08/19/02
Posts: 1691
Loc: New York City
Just out of curiosity. I've read that placing cable under a rug or carpet is dangerous because of heat buildup and also abrasion to the insulation?

What type of cable did you use and how is it protected?
Top
#28004 - 08/07/03 02:27 PM Re: Floor Outlets
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
It was a special cable made to run under carpet, looked very expensive, but don't remeber what type or brand it was.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#28005 - 08/07/03 02:59 PM Re: Floor Outlets
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
aldav -- You may be referring to 99 NEC Article 363 — Flat Cable Assemblies: Type FC.

http://www.delmarelectric.com/resources/sampchaps/electricity_1/E1-Chapter_18.pdf page 17

http://tnbelectricalworld.tnb.com/contractor/docs/versatrak_wiremgmt.pdf




[This message has been edited by Bjarney (edited 08-07-2003).]
Top
#28006 - 08/07/03 05:53 PM Re: Floor Outlets
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
I'd go along with Sven on that idea!.
This is the same reason why flex's shouldn't be run under mats.
The cable would be be safer from an electrical and fire safety point of view, if it was buried in conduit.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#28007 - 08/07/03 08:22 PM Re: Floor Outlets
amp-man Offline
Member
Registered: 06/23/01
Posts: 141
Loc: Sacto, California US of A
aldav53,

FCC (flat conductor cable) is allowed ONLY in commercial occupancies and ONLY under carpet squares!

The logic is that if there's a problem (meaning a fire), it'll be more apparent in an office setting, and people will be awake and able to evacuate faster.

As for the carpet square thing--I'm guessing that it's because carpet squares are not stretched during installation, like wall-to-wall carpet on a roll. Even though FCC glues down pretty well to cement slab, it could still be damaged by movement of carpet over it.

So, get out the rotp hammer and set it to "chip"...do the job right, do it safe!

Cliff
Top
#28008 - 08/07/03 09:30 PM Re: Floor Outlets
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
AMP-MAN,
Your right, they were carpet squares in a commercial building that I laid the flat cable. Looks like its cement cutting time.
Thanks,
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals