The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (LongRunner, Tjia1981), 178 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#2769 - 07/24/01 08:52 AM Opening breaker under rated load.
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
We recently had a situation where a water line burst and some of the falling water made it's way to above one of our MCCs.
I shut off the 600 amp main breaker, in order to de-energize the MCC. Typically our load is 200-300 amps (@ 480Y/277). Someone suggested that I should have shut off the individual breakers prior to opening the main. I see no reason do this, particularly in this situation, however I would like opinions on opening the main (not necessarily regularly) under it's rated load.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#2770 - 07/24/01 12:56 PM Re: Opening breaker under rated load.
Anonymous
Unregistered


I agree.
If I felt there was time, I would probably dump some branch loads first, not for the sake of the main CB, but for the sake of sensitive equipment out there somewhere that might not like being hammered.

With larger loads, dumping some stuff makes it more likely that certain types of switches will open and reduces the arc intensity when they are opened.

Top
#2771 - 07/24/01 01:37 PM Re: Opening breaker under rated load.
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Should be no problem, after all, that breaker should be able to interupt a fault several times higher than it's rating without doing damage.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#2772 - 07/24/01 05:05 PM Re: Opening breaker under rated load.
CanadianSparky Offline
Member

Registered: 03/05/01
Posts: 86
Loc: Alberta Canada
Wow, where i'm from I'd never even think about turning on a main without shedding the load first. You can break down a large inrush current by bringing on the loads a little bit at a time, especially with motor loads.

Top
#2773 - 07/24/01 05:14 PM Re: Opening breaker under rated load.
Anonymous
Unregistered


>turning on a main
He was talking about killing the main before it got wet.

Top
#2774 - 07/24/01 05:37 PM Re: Opening breaker under rated load.
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
 Quote:
Originally posted by CanadianSparky:
Wow, where i'm from I'd never even think about turning on a main without shedding the load first. You can break down a large inrush current by bringing on the loads a little bit at a time, especially with motor loads.


I understand your point and agree fully. Inrush can be minimized by bringing the load on gradually. I was discussing turning the power off, though.

Top
#2775 - 07/24/01 08:39 PM Re: Opening breaker under rated load.
sam Offline
Member

Registered: 01/02/01
Posts: 29
I believe you would have to make a really
Quick judgement call on that situation.
Hope no one was injured in this incident!

Top
#2776 - 07/25/01 03:49 AM Re: Opening breaker under rated load.
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
 Quote:
Originally posted by sam:
I believe you would have to make a really
Quick judgement call on that situation.
Hope no one was injured in this incident!

Luckily, nobody was hurt and equipment damage was minimal.
I would have preferred to shut the feeder off at the substation supplying our building. However, up until this incident, we did not have a key. I had to decide quickly what to do.

Top
#2777 - 07/25/01 11:16 AM Re: Opening breaker under rated load.
glenn35 Offline
Member

Registered: 07/21/01
Posts: 48
Isn't that one of the purposes the main was installed in the first place? To provide a means of disconnecting power quickly.
I see nothng wrong with it, because it is designed for that purpose.

The fire dept or the utility is not going to take time to go around and find other disconnects to releive load!

You did the right thing. Don't fret over it.

If the accusers were there then why didn't they do it? Or were they there and didn't know quite what to do? DUH DUH

Hind sight is 20/20 and talk is sometimes cheap.

[This message has been edited by glenn35 (edited 07-25-2001).]

Top
#2778 - 07/25/01 09:19 PM Re: Opening breaker under rated load.
frank Offline
Member

Registered: 05/29/01
Posts: 361
Loc: windsor ontario canada
gelnn35 is right and i belive pissing around de-energizing the load side of the MCC while water is leaking into the enclosure would be the worst course of action.ABOVE ALL THE MAIN CIRCUIT BREAKER BY FAR IS THE SAFEST PLACE TO DE-ENERGIZE OR ENERGIZE ANY LOAD THAT COULD COME UNDER A FAULT CURRENT CONDITION.The load at risk included the line side of the MCC.


[This message has been edited by frank (edited 07-26-2001).]