#27554 - 07/21/03 11:12 AM 1930s meter box
Chris Rudolph Offline
Member
Registered: 05/01/01
Posts: 160
Loc: Winter Park,Fl USA
I am in Central N.Y.for the summer(lots of dairy farms)and have been asked to install a new panel and some new ckts in a 140 year old farm house.This looked like a fairly simple job until I went to pull the meter and found that it is not the kind that plugs in but is in a covered weather proof box with a inspection glass for reading the power meter.
After removing the seal(with the POCO permission)I opened the hinged cover and found the GE meter had a glass cover,also with another seal on the metal ring that seals the glass to the meter, and the entire meter assy was hard mounted in the box.
It is very inconvient to schedule the POCO to disconnect the service because of the remote location,so I was thinking about disconnecting the two line sides of the meter,located under two lugs,while it is hot taking all the precautions(insulated gloves&tools, face shield).
Has anyone ever worked with this vintage(1930s) meter box before and if so, are there any tricks to pulling the meter that I am not able to see?Should I accept the inconvience and call the poco to disconnect the service?
Chris
Top
Work Gear for Electricians and the Trades
#27555 - 07/21/03 01:06 PM Re: 1930s meter box
Tom Offline
Member
Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Are there any exposed busbars with big nuts in the middle of the bar? If so, loosen the nuts with a nutrunner & this will turn off the power. I am still running across these really old meters, I think the POCO here calls them A Base meters.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#27556 - 07/21/03 03:11 PM Re: 1930s meter box
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
A frame meters are, IMO, best left alone, better to cut the service at the peak
( assuming an OH) Chris.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 72 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals