The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
1 registered (cableguy619), 212 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#27400 - 07/14/03 02:05 PM 90 degree column
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Just a quick question. Is there any time we can actually use the 90 degree column when sizing our wire, or do we always have to go with the 75 degree over 100 amps and the 60 degree under 100 amps. Thanks Steve.....

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#27401 - 07/14/03 02:54 PM Re: 90 degree column
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
You can always use the 90C column for sizing wire (if you have 90C insulation).

The problems occur when you want to terminate the wire. You can not connect any wire to a device unless the size is equal to or larger than the size determined by using the 75C (or 60C) column.

Also #10, #12, and #14 are limited to a maximum overcurrent protective device (30A 20A and 15A respectively) unless permitted by specific NEC articles (i.e. motor circuits).

A situation where I might use these data is:
Start at OCPD with 75C wire (i.e. 4-#4)
Go 3' to a junction/splice box
Use 90C wire as needed (i.e. 4-#6)
End at a junction/splice box
Go 3' to device with 65C wire (i.e. 4-#3)

Top
#27402 - 07/14/03 03:04 PM Re: 90 degree column
George Offline
Member

Registered: 02/23/02
Posts: 380
JBD ---

Let me ask question here.

Are most wire connectors rated at 90 degrees? I never looked at the temp rating of connectors before.

I never even considered that issue with can lights that require 90 degree wire.

Top
#27403 - 07/14/03 03:13 PM Re: 90 degree column
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Yes, most connectors and splice equipment are rated 90C or higher.

Also I should have said use 4' of wire (not 3'), as this is the length UL uses for heat rise testing.
http://www.idealindustries.com/wt/TwistOnWireConnectors.nsf

Top
#27404 - 07/14/03 04:22 PM Re: 90 degree column
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I have installed larger equipment that has been 90C rated Square D 3000 amp breakers specifically.

Also when you need to do ampacity adjustments for temperature or number of conductors you can start with the 90C column. Once you do your derating you check the derated figure against the column for the temperature of the termination or wire you are using and use the lowest figure.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#27405 - 07/14/03 04:29 PM Re: 90 degree column
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
From this non-electrician...

Wet locations are always limited to the 75° column, correct?

Top
#27406 - 07/14/03 07:59 PM Re: 90 degree column
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
So If I understand it right, there is no place that I can use the 90 degree column to size my wire from the OCPD to the termination device. Looks like the manufactures would be made to make their lugs suitable for the maximum allowable degree of wire So the 90 degree table is no good unless you want to make a bunch of junction boxes??? Don't seem right somehow... Thanks for the input... Steve

Top
#27407 - 07/14/03 08:25 PM Re: 90 degree column
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
TG — Many insulated conductors are 75°C wet and 90°C dry, but two exceptions in (99)NEC table 310-13 are RHW-2 and XHHW-2 that are rated 90°C for both. A common application aside from termination-temperature limitations is as a “starting point” for table 310-16+ ampacity-table temperature adjustments and §31O-15 ‘more than 3 conductors’ adjustment.

Top
#27408 - 07/15/03 02:36 AM Re: 90 degree column
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
sparkync

 Quote:
there is no place that I can use the 90 degree column to size my wire from the OCPD to the termination device


It is not as bad as that, as I said there is some equipment out there rated 90C.

The real gift of the 90C column is when we have to derate.

Lets say you are running 9 current carrying conductors in a raceway or in a bundle of cables.

310.16 lists 12 AWG at 30 amps in the 90C column which is the figure you can start with for derating.

Table 310.15(B)(2)(a) requires a 70% adjustment for that many conductors.

30 amps x .7 = 21 amps.

So now after derating you can still use these conductors for a 20 amp circuit.

If you did this derating starting at 20 amps

20 x .7 = 14 which would mean you would need to use a 15 amp breaker for these conductors.

240.4(B) is the article that allows the next standard size breaker to be used in most instances.

Bob

Oh I should mention that 14, 12 and 10 AWG are not "rated" 15, 20 and 30 amps, (they are rated higher) the requirement that we use 15, 20 and 30 amp OCPDs on these size wires is 240.4(D) which does not change the rating of the conductors just the OC protection.


[This message has been edited by iwire (edited 07-15-2003).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#27409 - 07/15/03 12:17 PM Re: 90 degree column
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
ThinkGood,
Wet location wire with a "-2" after the wire type letters is 90°C wet or dry.
don
_________________________
Don(resqcapt19)

Top