The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (crselectric, mbhydro), 232 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#27322 - 07/10/03 04:12 PM Anybody ever splice service cable?
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
I've got a customer that is having a water problem entering through the service which enter the house below grade in the basement. From there they have 4 150 amp panels branching from a gutter. To solve the problem I need to rebuild the service, putting all the disconnects outside and re-entering above grade. All currect service cables are fairly new and are 4 conductor.

Can I splice each of these cables in a j-box or gutter? I can't find a code prohibitting splicing the main, I've just never had to do it.

Thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#27323 - 07/10/03 04:37 PM Re: Anybody ever splice service cable?
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Where is the meter in this arrangement?
_________________________
Ron

Top
#27324 - 07/10/03 04:39 PM Re: Anybody ever splice service cable?
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
If it is an underground service lateral conductor, then see 230.33.
_________________________
Ron

Top
#27325 - 07/10/03 04:45 PM Re: Anybody ever splice service cable?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
230.46 Allows service conductors to be spliced.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#27326 - 07/10/03 04:59 PM Re: Anybody ever splice service cable?
arseegee Offline
Member

Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
David, I had a plumber run a saw thru a 4/0 SER about three years ago. He had to move his pipes and thought it would be easier to use his 18v circular saw than a drywall saw (not a real sharp guy). Well he was VERY lucky because when he went thru the SER it was rolled where he only cut the ground and neutral. The ground was cut clear through and about 50% of the neutral conductor was missing.

The panels were between floors and repulling the entire cable was out of the question but i was able to pull a new cable to an accesible point and splice the entrance.

After a discussion with the inspector, I used a 12"x12"x4" galvanized j box with two 2" nwt (romex) connectors, a 2/0 double lug for my grounding (and bond)bolted to the enclosure and three 2 conductor Ilsco insulated tap connectors for the neutrals and hots.

A hour later i had a bill for the plumber.

Top
#27327 - 07/10/03 06:09 PM Re: Anybody ever splice service cable?
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Thanks Guys,

The meter is outside, but inside the basement is a large can with pad locks from the poco. From there it branches to a gutter and a 3" PVC comes out the bottom of the poco can. The water leaks from a joint in the 3" pvc. It is definately a potential hazard. The homeowner thinks the poco is responsible since they own the can. I think the homeowner will ultimately have to pay to update. I really can't see why it was done this way to begin with. Also, I'm sure the conductors from the meter to the poco can are undersized, since another contractor added 2 of the 150 panels a year or so ago without a permit.

Top
#27328 - 07/10/03 06:26 PM Re: Anybody ever splice service cable?
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
Water entering the service entrance is a disaster waiting to happen...