The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 84 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#27269 - 07/07/03 04:00 PM Hot Bus in the Motor City
MikeW Offline
Member

Registered: 06/03/02
Posts: 39
Loc: Michigan
Hello everyone! First time I visited this site in a couple of months. My question is do any of you install swing-jacks into a hot 480 volt bus? I was told in our plant the policy is you can install up to 200 amp bus plug without shutting off bus. I do it and I always megger out the switch first. Am I being stupid. My boss told me if I felt uncomfortable with installing them hot then we would have the buss shut off. The problem with that is it is a big inconvenience to everyone else in a large factory and during production it is nearly impossible.

I would like to hear your opinions. Thanks.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#27270 - 07/07/03 05:33 PM Re: Hot Bus in the Motor City
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
I wouldn't hesitate to check phase-to-phase and phase-to-ground...six tests. They should all be infinite. [The available short-circuit current on the bus-plug line terminals is not dependent on the rating of the bus plug.]

You might obtain the published installation literature from the duct manufacturer.

Top
#27271 - 07/07/03 06:34 PM Re: Hot Bus in the Motor City
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
If you install the switches into a hot bus, you must be wearing PPE rated for the arc-blast that could result if there was some type of problem.
Don
_________________________
Don(resqcapt19)

Top
#27272 - 07/07/03 07:31 PM Re: Hot Bus in the Motor City
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Even though “many do it,” I don’t think live jacking in of circuit breakers, for example, in energized I-line panelboards is condoned.

In an IEEE journal, there is some commentary that seems to discourage intentional exposure of live parts in low-voltage industrial electrical systems.

UL standards for distribution equipment are written with the understanding that abnormal conditions will occur in electrical systems. Abnormal conditions may include explosive arcing and flaming of materials, either causing or resulting from heavy overcurrent conditions including arcing faults to ground and phase-to-phase short circuits.

It should be noted that enclosures for low-voltage electrical distribution equipment are also evaluated by the short-circuit testing of equipment they contain. Under these standard testing conditions, the enclosures are expected to retain general structural integrity and, in some cases, cotton indicators are used to show that nearby materials would not ignite. However, these tests in no way evaluate the ability of these enclosures to contain abnormal arcing or flaming from conditions other than interruption of a bolted fault. Further, equipment will not protect people working inside of it during the abnormality.
IEEE TRANSACTIONS ON INDUSTRY APPLICATIONS, V35 N1, JANUARY/FEBRUARY 1999

Anecdotally, there are reports of serious disasters {er, burndowns} from live removal/installation of plug-in "starter buckets" in MCCs. I don’t see bus-plug removal/installation being much different.




[This message has been edited by Bjarney (edited 07-07-2003).]

Top
#27273 - 07/09/03 03:59 AM Re: Hot Bus in the Motor City
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Food for thought...

We had (at another location) an electrician modify an MCC bucket by installing an accessory on the back plate.
He used screws that were longer than the factory screws.
When he attempted to install the bucket, the screws contacted the buss, and an arc blast occured.
He lingered in the burn center for 4 days before succumbing.
And THAT was the impetus for our new Electrical Safety Program which borrows heavily from NFPA 70E.
Be aware, please