#27258 - 07/06/03 08:39 PM OH Service
Mike_Riverside Offline
Member
Registered: 08/18/02
Posts: 33
In a 200A OH service tri-plex will be 1/0, should the riser also have 1/0, or 3/0 because it is in conduit? Riser will be CU THWN-2, Sun Resist.

[This message has been edited by Mike_Riverside (edited 07-06-2003).]
Top
Work Gear for Electricians and the Trades
#27259 - 07/07/03 12:11 PM Re: OH Service
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Mike,

If this is a service for a dwelling, 2/0 copper is fine, if it is for any other occupancy, you'll need at least 3/0 copper.

Tom