#26845 - 06/24/03 01:42 PM Need help with comm. building load calc
qopanel Offline
Member
Registered: 07/09/02
Posts: 17
18,850 sq foot building with 12 units. 120/240v single phase. Cant get three phase. This is the base building with future buildouts to come at later dates. There will be 12 ac units drawing a max of 30 amps each. 12 120v 15 amp electric water heaters and small 120v furnaces. 12 exit lights and 24 em lights. 40 outside soffit cans with 120v 60 watt bulbs. the rest of the building is build out as they are sold. I dont know how to figure the rest of the genaral lighting and recptical load for power company. Is there a standard I should use for not knowing the futrue build outs. The spaces will all be professional type use (doctors, lawyers , office space)
Top
Work Gear for Electricians and the Trades
#26846 - 06/24/03 04:53 PM Re: Need help with comm. building load calc
CDN_ELECTRICIAN Offline
Member
Registered: 01/22/03
Posts: 73
Loc: Concord,Ontario,Canada
Well, hope this helps as much as I can!

Section 220 for NEC has all the info you need for calculations in the United States
and
Section 8 in the CSA has the info you need for Canadian calculation
Top
#26847 - 06/24/03 07:35 PM Re: Need help with comm. building load calc
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
I don't know about other areas, but before I start a job of this magnitude, I need approved electrical engineer drawings.

Doesn't the Building Dept have to approve of the electrical drwng/design, before issuing a building permit?
Top
#26848 - 06/25/03 02:09 AM Re: Need help with comm. building load calc
nesparky Offline
Member
Registered: 06/21/01
Posts: 642
Loc: omaha,ne
Sugggest you offer a couple of different packages for this shell building. One would install 100 amp panels in each new unit, hook up the known load for that unit, 1 recepticle outlet under the panel, and maybe some lights.
Another package would offer larger panels and more outlets.
See what the owner will pay for and plan accordanly.
_________________________
ed
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals