The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 192 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#26722 - 06/18/03 10:01 PM exam question
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
question; an office building has a total area of 50,000 sf, the actual number of gen-purpose receptacle outlets is unknown and the connected load equals the calculated load. how many 120 volt,2-wire,20 amp branch circuits are for the lighting and receptacles ? I missed this one on a practice exam. the options were,21,92,112,or 118. can someone could show me the calculations,.... thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#26723 - 06/19/03 05:37 AM Re: exam question
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
How about 92...

50,000 sq. ft. X 3.5 VA (from Table 220.3A)=175,000 VA required.
175,000/1920 (16 amps continuous X 120 Volt)= 91.145

What did you get?


[This message has been edited by Redsy (edited 06-19-2003).]

Top
#26724 - 06/19/03 10:23 AM Re: exam question
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
thanks,redsy, I fogot to change the 20amp ckt to 1920 va.

Top
#26725 - 06/19/03 10:27 AM Re: exam question
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
do you have an example on using table:220.34 for selecting feeder/service conductors for a school, there are no examples for this in the nec handbook ?

Top
#26726 - 06/19/03 11:42 AM Re: exam question
dana1028 Offline
Member

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
Look at Table 220-3(a), if you look at the table for office buildings it gives you a value of 3.5 v/a per sq. foot BUT there is a footnote 'b'...if you read this footnote it indicates you must ADD an additional 1 v/a per sq. ft. for general-purpose receptacle outlets where the actual number of receptacle outlets is UNKNOWN.

Therefore you have a total v/a per sq. ft. of 4.5 calculated as follows:

3.5 v/a x 50,000 sf. = 175,000 va x 125% (lighting is considered a continuous load) = 218,750 v/a + 50,000 v/a (1 v/a per sf for unknown receps) = 268,750 va/120v = 2239.58A /20A ckt rating = 112 circuits

Go to RKeiss' website (www.elec-toobox.com), in his 'Code Quiz' section, May, 2001, quiz question #6 - he takes you through the steps of computing the answer for the same situation you asked.

[This message has been edited by dana1028 (edited 06-19-2003).]

Top
#26727 - 06/20/03 06:16 PM Re: exam question
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Good catch, dana.
But, I don't understand why the 125% is only added to the basic 3.5 va/sq.ft. and not the additional 1 va/sq.ft.

I still would suggest the following...

50,000 x 4.5 = 225000
225,000 / 1920(80% of 120x20) = 117.19 (118 ckts.)
OR...
50,000 x 4.5 x 125% = 281,250
281,250 / 2400 (120x 20) = 117.19 (118 ckts.)

Top
#26728 - 06/20/03 07:03 PM Re: exam question
dana1028 Offline
Member

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
because they are applying the 1 va to the recep load and applying the 3-1/2 va to the lighting load...lighting loads are considered continuous loads in non-dwelling occupancies....if you read the title to the table " General Lighting Loads"

...per your calculations - 117.19 is rounded down, not up (see 220-2b)...117 is not one of the options for an answer.



[This message has been edited by dana1028 (edited 06-20-2003).]

Top
#26729 - 06/21/03 04:44 AM Re: exam question
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Thanks for the clarification, dana.

Top