The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
Search Function
by Admin
01/18/17 11:13 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 32
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
2 registered (Admin, ComputerWizKid), 0 Guests and 188 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#26569 - 06/15/03 01:21 PM Megging circuit breakers
Elzappr Offline
Member

Registered: 12/20/01
Posts: 273
Loc: Oregon
Anyone know the scoop about how to safely meg a circuit breaker? I often wonder if all the electronics that are part of circuit breakers these days would mess up megger readings. Suppose, for example, someone wants to meg out a circuit from a supply bus bar, through a distribution panel circuit breaker, through the feeder conductors..stopping at the open branch circuit breaker. Is this a practice which might show misleadingly low resistance numbers due solely to the feeder circuit breaker's electronic trip package?
Are there limits to how high the test voltage should be? Would a 1kV test voltage mess up, or interact with the trip unit, in a 240 volt breaker?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#26570 - 06/15/03 04:09 PM Re: Megging circuit breakers
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
It’s probably a little more common to use 500VDC on 240/208V stuff. As for readings, it’s primarily a matter of experience, and comparing pole-to-pole readings for lack of any IR history. In electronic-trip molded-case breakers, if there is no external communications or relaying, the meg tests generally shouldn’t damage anything—but get your mitts on the breaker instruction pamphlet for any warnings.

Biddle sells a booklet titled “A Stitch in Time” that covers the subject in a practical manner.

Obviously, megging a VFD would be suicide.

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals