#26560 - 06/15/03 12:51 AM MC cables to conduit wiring
Nagelec Offline
Member
Registered: 06/08/03
Posts: 12
Loc: Sharjah, UAE
We intend to use the MC (Metal clad) cable on cable trays in the existing offshore platform which has presently the conduit installations. I would like to know how the MC cable (Aluminium sheathed) shall enter from Div.1 area into the MCC room (safe area). All the entries to the existing MCC room is as conduit entry. Can any one please clarify how this conversion (Cable to conduit)takes place?
Top
Work Gear for Electricians and the Trades
#26561 - 06/15/03 04:15 PM Re: MC cables to conduit wiring
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Are you referring to using MC-HL cable(which is suitable for Div. 1 locations)in the Classified area ?
If so, why convert at all?
Why not run the MC cable right into the MCC?
Either way, proper cable seals will be required. And cable the terminator/seal fittings for MC-HL are about $50-60.00 ea. for 3/4" size.



[This message has been edited by Redsy (edited 06-15-2003).]
Top
#26562 - 06/15/03 05:39 PM Re: MC cables to conduit wiring
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
Offshore and Aluminum sheathed, Just don't go together. A short length of alum mc was used for a quick repair, It lasted for about 3 months. It looked like it was there for years.

[This message has been edited by LK (edited 06-15-2003).]
Top
#26563 - 06/15/03 07:19 PM Re: MC cables to conduit wiring
Vickrey Offline
Member
Registered: 05/29/03
Posts: 10
Loc: Fort Stockton, Texas,USA
Run ridgid from the Div 1 area to the unclassified area and feed the cable through the conduit.
Top
#26564 - 06/16/03 12:43 AM Re: MC cables to conduit wiring
Nagelec Offline
Member
Registered: 06/08/03
Posts: 12
Loc: Sharjah, UAE
Thanks for your replies.

Hi Redsy,
Yes it is MC-HL Aluminium sheathed cables to use in Div.1 Area. The cable has to enter into false flooring of MCC room from bottom, then run in the false flooring and get terminted into the MCC/DB mounted on the false flooring. So I want suggesstion about 1)how to enter into the false flooring, 2)how to run in the false flooring (i.e whether in the spliced form on cable trays until the MCC/DB) and 3)what are all the fittings required for proper entry into the false flooring (i.e gland, seals etc). Please clarify.

Hi LK,
Do you mean Aluminium sheathed cables are not suitable for offshore applications?

Hi Vickrey,

What is ridgid and how we can use the same for my requirement. Can you please elaborate?

Thanks in advance.
Top
#26565 - 06/16/03 04:26 AM Re: MC cables to conduit wiring
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Nagelec,
Do you have a 2002 Crouse-Hinds catalog?
MC-HL used in Hazardous Locations needs to be terminated with TMCX fittings. (pages 76-77).
Try to run the cable directly to the MCC. You will need termination fitting at each end. It may be difficult to properly install the TMCX at the underside of the MCC, as you need some working room to install it.
Im not familiar with your false flooring, so I can't help, cable tray mey be necessary due to the support intervals required for MC cables (6').
Top
#26566 - 06/16/03 04:38 AM Re: MC cables to conduit wiring
Nagelec Offline
Member
Registered: 06/08/03
Posts: 12
Loc: Sharjah, UAE
Hi Redsy,

Thank you for your reply. We are working on this issue to solve this. Before connecting the cable to MCC, the cable has to enter from Div 1 area (where electrical equipment is located) into false floor which is unclassified (safe area). So the cable has to be properly sealed before entering into the falseflooring.
Top
#26567 - 06/16/03 06:40 AM Re: MC cables to conduit wiring
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Nagelec,

I don't believe that cable needs to be sealed within 10' of a classification boundary, as conduit does, per 510.5 (A)(4). The NEC doesn't specify, in 501.5(D), a maximum distance from where the classification changes to where a CABLE seal is required. This is probably due to the impervious jacket on MC-HL. I believe you can run the (intact) cable right up to the MCC and install the seal/terminator fitting on the MCC.
Top
#26568 - 06/16/03 04:04 PM Re: MC cables to conduit wiring
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
Yes not a good idea for platform work,if this in in the mcc room then conditions should be ok. not on any of the deck area. At one of our safety conf. the eng for the offshore operations showed us pictures of weather worn electrical. wow, you must have some intresting projects.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals