Hello my Father owns a buisness in La Mirada, Ca. and we recently looked into the T-Bar ceiling.
I'm currious, how are ceiling fans suppose to be mounted? Ours shakes!
Top
Work Gear for Electricians and the Trades
#2630 - 07/16/01 05:38 PM Re: T-GRID & CEILING FANS
johnd24 Offline
Member
Registered: 07/11/01
Posts: 62
Sounds like your blades r unbalanced.I use strut and allthread to mount my fan box for a drop ceiling.Attached to the cieling of course not the grid work.
Top
#2631 - 07/16/01 09:13 PM Re: T-GRID & CEILING FANS
RUEZ2BE Offline
Junior Member
Registered: 07/16/01
Posts: 4
Loc: WHITTIER, CALIFORNIA,USA
Quote:
Originally posted by johnd24:
Sounds like your blades r unbalanced.I use strut and allthread to mount my fan box for a drop ceiling.Attached to the cieling of course not the grid work.
Top
#2632 - 07/16/01 10:11 PM Re: T-GRID & CEILING FANS
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
RUEZ2BE,

Hello!

Not sure about any special requirements for California. There are special kits sold for this application involving chains. I've also seen boxes supported by threaded rod from structural ceiling above (steel).

Bill
Top
#2633 - 07/17/01 05:13 AM Re: T-GRID & CEILING FANS
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
The strut/rod hanger is fine, but probably this is a good candidate for seismic bracing. These consist of T-bar wires splayed from the attachment point of the box out @ about 45° to the structure above. (notice that I only said probably, it depends on your particular circumstances).
The shaking is due to blade imbalance. You can buy a balancing kit @ Home Depot. It consists of adhesive backed weights, and a set of instructions.
Top
#2634 - 07/17/01 06:48 AM Re: T-GRID & CEILING FANS
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
The quality of the fan may have something to with it also. I have seen some cheap fans gently vibrate without the blades attached. Probably has to with the balance of the motor and its mounting in the enclosure.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals