The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 84 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#26172 - 05/31/03 08:42 AM solenoid question
Nevin Offline
Member

Registered: 05/28/01
Posts: 31
Loc: Lititz PA 17543
I have an electrically operated hydraulic valve. It has 2 solenoid on each end and is self centering when all elecricity is removed.

During normal operation the solenoid on one side is energized, moving the hydraulic spool over. When electicity is removed and applied to the other solenoid, the spool moves in the other direction.

My question is, If electricity were applied to both solenoids simultainiously (due to malfunctioning or incorrectly setup equipment), would it cause coil burn out? If it does, why does it? Does it overheat due to the iron core not being pulled into the center of the coil?
We had this senorio happen where due to setup error both coils were energized at he same time and after a short period of time one of the coils failed. However before the coil failed, the valve "seemed" to operate as normal except it would never stay in neutral. Apparently the one coil was stronger then the other and over rode the weaker one.

Does anyone have any insight on this?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#26173 - 05/31/03 10:21 AM Re: solenoid question
NJwirenut Offline
Member

Registered: 09/15/01
Posts: 816
Loc: Bergen County, NJ
If the core is already at one end of the travel, (one coil energized) and the other coil is then energized, the second coil will not have enough force to pull the core to center. The force from a solenoid is a function of core position, with maximum force available at the end of travel.

So the core will remain at one end of travel, and the other coil will overheat due to excessive current (caused by the core not moving to complete the magnetic circuit).

Top
#26174 - 05/31/03 11:02 AM Re: solenoid question
Vickrey Offline
Member

Registered: 05/29/03
Posts: 11
Loc: Fort Stockton, Texas,USA
An enregized solenoid coil will burn up with out at least a partial presents of the core. I believe you were correct about what happened. When one coil finally gave up the smoke the other got the core The surviving coil is probablly degraded and could have a shortend life expectancy. If this is a safety item I would replace them both.
I've seen coils removed from the assembly to change the core/shuttle (which is a high fail mechanical part) and during this time the plant energized the coil. Naturally when everything was put back together it didn't work because the coil was fried.

Top
#26175 - 06/02/03 08:51 AM Re: solenoid question
Nevin Offline
Member

Registered: 05/28/01
Posts: 31
Loc: Lititz PA 17543
Thanks for the replies.
That confirms my suspicions!

Top