The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#25584 - 05/13/03 11:54 AM Tripping arc-fault breakers on generator backup power
retiredGuy Offline
Junior Member

Registered: 05/13/03
Posts: 1
Loc: Conway, NH, USA
Hello All,

I just installed a Generac 7,000 watt generator with a Connecticut Electric Switch
Energen Manual Transfer Switch Model 10-7500.
Two of the circuits on the Manual Transfer Switch are wired to supply power, in a power-loss situation, to two bedroom arc-fault circuit breakers in this Square D distribution panel. The Arc-fault breakers trip whever the generator supplied power is placed on the circuits.

Is it possible to wire to these circuits so as not to trip the distribution panel arc-fault breakers?
Is it likely that I have made a mistake????
Should these circuits be wired differently than all the others???

Thank you for your help,

Ron Gabaree,
Master Electrician/ Contractor

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#25585 - 05/13/03 02:53 PM Re: Tripping arc-fault breakers on generator backup power
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Verify that, in the transferred condition, the (one) neutral-to-ground bonding jumper is intact. [For a typical residential system, that should almost always be the case regardless of the transfer-switch position.]

Top