#25539 - 05/12/03 04:11 PM Suplemental grounding electrode
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
I read the NEC to say that if you use an underground water pipe as your grounding electrode you must suplement it with an addtional electrode which must be less than 25 ohms (250.56). I have only been installing one rod for the suplemental and that has been fine with inspectors, till now. I ran into one that wants two since I can't verify less than 25 ohms. I beleive he is right and have no problem with it but another electrician I know says he is just busting my chops. He seems to think the inspector can not say it is or is not less than 25 ohms thefore no addtional rod is required. What's the real deal. Thanks, Scott
Top
Work Gear for Electricians and the Trades
#25540 - 05/12/03 04:39 PM Re: Suplemental grounding electrode
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
They've been making us use 2 rods for a while around here. It's not that expensive, so I don't see a reason to argue about it, just do it.
Top
#25541 - 05/12/03 07:00 PM Re: Suplemental grounding electrode
NorthernLights Offline
Member
Registered: 03/12/03
Posts: 10
Loc: Massachusetts
One of the towns in my area asks for 2 ground rods. When I ask about it, he threatened to actually bring out test gear to prove me wrong. I put in the 2 rods......like someone said, it's not that expensive and not worth the argument. This is not one of those arguments worth pursuing.
Top
#25542 - 05/12/03 07:12 PM Re: Suplemental grounding electrode
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
For what it's worth....
We have been enforcing the 2 rods or <25 ohms for a while. You get the occasionsl argument from an EC, but my usual response is

Ground rod testing equipment is about $2000.00. You probably need a day to familiarize yourself with the gear, and some time to perform the test.
A second rod, clamp, wire, is about $20.00

Make it a financial decision.

PS: NJ interpertation of "let the AHJ test it, and prove it's NG" does not fly. The proof of test results is upon the installer, be it the homeowner or the EC.

Nuff said
John
_________________________
John
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:08 AM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
2 registered (Fidellis, Admin), 141 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/07/03
Posts: 84

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals