The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 261 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#25539 - 05/12/03 04:11 PM Suplemental grounding electrode
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
I read the NEC to say that if you use an underground water pipe as your grounding electrode you must suplement it with an addtional electrode which must be less than 25 ohms (250.56). I have only been installing one rod for the suplemental and that has been fine with inspectors, till now. I ran into one that wants two since I can't verify less than 25 ohms. I beleive he is right and have no problem with it but another electrician I know says he is just busting my chops. He seems to think the inspector can not say it is or is not less than 25 ohms thefore no addtional rod is required. What's the real deal. Thanks, Scott

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#25540 - 05/12/03 04:39 PM Re: Suplemental grounding electrode
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
They've been making us use 2 rods for a while around here. It's not that expensive, so I don't see a reason to argue about it, just do it.

Top
#25541 - 05/12/03 07:00 PM Re: Suplemental grounding electrode
NorthernLights Offline
Member

Registered: 03/12/03
Posts: 10
Loc: Massachusetts
One of the towns in my area asks for 2 ground rods. When I ask about it, he threatened to actually bring out test gear to prove me wrong. I put in the 2 rods......like someone said, it's not that expensive and not worth the argument. This is not one of those arguments worth pursuing.

Top
#25542 - 05/12/03 07:12 PM Re: Suplemental grounding electrode
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
For what it's worth....
We have been enforcing the 2 rods or <25 ohms for a while. You get the occasionsl argument from an EC, but my usual response is

Ground rod testing equipment is about $2000.00. You probably need a day to familiarize yourself with the gear, and some time to perform the test.
A second rod, clamp, wire, is about $20.00

Make it a financial decision.

PS: NJ interpertation of "let the AHJ test it, and prove it's NG" does not fly. The proof of test results is upon the installer, be it the homeowner or the EC.

Nuff said
John
_________________________
John

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals