The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#25350 - 05/06/03 02:47 AM votage between neutral and ground
wiking Offline
Junior Member

Registered: 12/13/02
Posts: 32
Loc: Florida, USA
Have you ever checked the voltage between neutral and ground and gotten somethng like 1.7 volts? What could be the cause of this? Could it be perhaps loose or corroded connection where the neutral is bonded to ground, or perhaps the neutral is slightly coming into contact with ground somewhere downstream? Perhaps induced voltage? Or maybe something in equipment?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#25351 - 05/06/03 08:02 AM Re: votage between neutral and ground
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Where exactaly are you measuring this voltage? If you are at the load end of the circuit, you are really measuring the voltage drop on the grounded conductor.
Don
_________________________
Don(resqcapt19)

Top
#25352 - 05/07/03 02:43 AM Re: votage between neutral and ground
wiking Offline
Junior Member

Registered: 12/13/02
Posts: 32
Loc: Florida, USA
I should have explained that this was measured at a recepticle. A guy i work with was asking me because he put in a recepticle and was hot checking it and between the neutral and ground on the recepticle he read 1.7 volts. I hadn't considered voltage drop. Thanks for the reply.

Top
#25353 - 05/07/03 05:35 AM Re: votage between neutral and ground
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Also consider the possibility of phantom voltage as a result of the impedance of your meter.
But I agree with Don, probably voltage drop on the grounded conductor.


[This message has been edited by Ron (edited 05-07-2003).]
_________________________
Ron

Top
#25354 - 05/13/03 06:01 PM Re: votage between neutral and ground
wiking Offline
Junior Member

Registered: 12/13/02
Posts: 32
Loc: Florida, USA
Thank you for your replies. I am trying to gain a little understanding about this and since you mention impedance and voltage drop as the likely source of this measurement, I am wondering if the meter is applying a voltage across the wires for measurement purposes or how this occurs. I assume the meter measures voltage thru induction across coils? Is this correct? From what source is the voltage drop reading being supplied since the neutral and grounded conductor should be at the same potential? Or perhaps there is voltage on the neutral because of a load downstream?

Top
#25355 - 05/14/03 05:07 AM Re: votage between neutral and ground
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The voltage drop would be on the grounded (neutral) conductor caused by other loads that are connected to it. A 10 amp load on 90' of #12 copper would result in about 1.8 volts of drop on the grounded conductor.
don
_________________________
Don(resqcapt19)

Top
#25356 - 05/14/03 02:51 PM Re: votage between neutral and ground
wiking Offline
Junior Member

Registered: 12/13/02
Posts: 32
Loc: Florida, USA
My apologies.....I actually meant grounding conductor in the previous post and I really do know how to spell voltage.

Top