#25239 - 05/01/03 05:23 PM Bonding panels
rowd Offline
Member
Registered: 09/13/02
Posts: 31
Loc: Park Forest, Illinois, USA
Can someone give me a inspectors definition of "bonding". I have 3 main panels in a residential building. The inspector says he wants the panels bonded together.
I thought they were "bonded together" already as the Metal pipe for each panels feeder wire goes back to the meter sockets which are "bonded" together with pipe and locknuts.
I don't understand what he's looking for when he says "bonded together".
Top
Work Gear for Electricians and the Trades
#25240 - 05/01/03 05:58 PM Re: Bonding panels
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
Bonding bushing at the meter sockets?
_________________________
Ron
Top
#25241 - 05/02/03 03:04 AM Re: Bonding panels
zapped208 Offline
Member
Registered: 02/18/03
Posts: 196
Loc: Somewhere in USA
rowd,- More than likely he is wanting a bonding jumper between all 3 panelboards, 2002 NEC 250.66
_________________________
Shoot first, apologize later.....maybe
Top
#25242 - 05/02/03 04:17 AM Re: Bonding panels
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Did you install a separate EGC?
Generally, the conduit feeding the panels, if continuous and tight should be sufficient to serve as an EGC and a bonding means.
See 250.96
Are there any eccentric or concentric rings left at the conduit connection point? Although bonding bushings are only required for Services, per 250.92, and 250 Volts or more, per 250.97, he may have concerns about loose conduit connections.
Ask him for specific references!

[This message has been edited by Redsy (edited 05-02-2003).]
Top
#25243 - 05/04/03 06:48 PM Re: Bonding panels
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Rowd,

I would call the AHJ and ask him. We would only be guessing as to what he really means. As an AHJ I don't mind when someone calls me up and asks, "What did you mean?" I would be more than happy to explain to him what I saw, and what needs to be done in order to get the job done. After all he might be right and I just didn't see something.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 91 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals