#25239 - 05/01/03 08:23 PM Bonding panels  
rowd  Offline
Member
Joined: Sep 2002
Posts: 31
Park Forest, Illinois, USA
Can someone give me a inspectors definition of "bonding". I have 3 main panels in a residential building. The inspector says he wants the panels bonded together.
I thought they were "bonded together" already as the Metal pipe for each panels feeder wire goes back to the meter sockets which are "bonded" together with pipe and locknuts.
I don't understand what he's looking for when he says "bonded together".


Work Gear for Electricians and the Trades

#25240 - 05/01/03 08:58 PM Re: Bonding panels  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Bonding bushing at the meter sockets?


Ron

#25241 - 05/02/03 06:04 AM Re: Bonding panels  
zapped208  Offline
Member
Joined: Feb 2003
Posts: 196
Somewhere in USA
rowd,- More than likely he is wanting a bonding jumper between all 3 panelboards, 2002 NEC 250.66


Shoot first, apologize later.....maybe

#25242 - 05/02/03 07:17 AM Re: Bonding panels  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Did you install a separate EGC?
Generally, the conduit feeding the panels, if continuous and tight should be sufficient to serve as an EGC and a bonding means.
See 250.96
Are there any eccentric or concentric rings left at the conduit connection point? Although bonding bushings are only required for Services, per 250.92, and 250 Volts or more, per 250.97, he may have concerns about loose conduit connections.
Ask him for specific references!

[This message has been edited by Redsy (edited 05-02-2003).]


#25243 - 05/04/03 09:48 PM Re: Bonding panels  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Rowd,

I would call the AHJ and ask him. We would only be guessing as to what he really means. As an AHJ I don't mind when someone calls me up and asks, "What did you mean?" I would be more than happy to explain to him what I saw, and what needs to be done in order to get the job done. After all he might be right and I just didn't see something.



Member Spotlight
richard
richard
L.I. New York
Posts: 94
Joined: August 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7653 MB (Peak: 0.9027 MB) Zlib enabled. Server Time: 2017-03-27 16:33:33 UTC