The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 280 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#25169 - 04/29/03 03:02 PM rooftop a/c unit
frank Offline

Registered: 05/29/01
Posts: 361
Loc: windsor ontario canada
Opened up year old roof top A/C unit on a new building to find a crookedly mounted and NEW 150a breaker with #3 wire on the line side and about 6 wires in each load side terminals? Nameplate values call for a 100a brk and fla is 82a 600v .Back in the mechanical room we find the line side fused at 125a with #3 wire .The unit symptoms are intermittent tripping of the 150a in unit breaker.Other then the horrid wiring around this breaker the unit is factory and seems to be running well.I don't know what to think. Did someone swipe the splitters and switch breakers? Did it come from the factory like this ? I was working on it with a refrigeration mechanic and tightened all the terminal screws ect and now it has not tripped since.The whole installation looks very unique to say the least.

[This message has been edited by frank (edited 04-29-2003).]

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#25170 - 05/03/03 12:49 AM Re: rooftop a/c unit
Trumpy Offline


Registered: 07/05/02
Posts: 8532
Loc: SI,New Zealand
To be honest, I wouldn't think that a factory made unit would be as rough as that, they have to pass Quality Control examinations before they leave the factory.
I'd say some else has "had a go at it" since it was installed.
But them six wires in each of the load-side terminals sound a bit suspect, to say the least!.
Let's face it, these days if you're not young, you're old - Red Green grin