The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
Yesterday at 09:52 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
0 registered (), 0 Guests and 164 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#24740 - 04/21/03 11:05 PM Ridgid PVC
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Can PVC schedule 40 marked ridgid, be run 6" underground just like steel ridgid?
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#24741 - 04/22/03 03:18 AM Re: Ridgid PVC
zapped208 Offline
Member

Registered: 02/18/03
Posts: 201
Loc: Somewhere in USA
Table 300.5 Underground Installations,(A) Minimum Cover Requirements, should have what you need to know.
_________________________
Shoot first, apologize later.....maybe

Top
#24742 - 04/22/03 03:41 AM Re: Ridgid PVC
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
No you can not, the code refers to PVC as RNC or Rigid Nonmetallic Conduit but that does not mean the rules of RMC (Rigid Metal Coduit) apply.

As zapped said, Table 300.5 gives the info which varies depth depending on location.

Under traffic 24" (except dwellings 18")

Generally 18"

Bellow 2" cement slab 12"

Bellow 4" cement slab 4"

Under a building 0"