#24729 - 04/21/03 09:04 PM GFCI
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
When replacing an existing outlet with a GFCI the rules are no ground then no ground downstream. when there is a full size ground then connect all grounds. What is the accepted practice when a reduced size 16ga bare ground is connected. Do you open the ground connection, continue the ground downstream; or connect the reduced ground on all devices
Top
Work Gear for Electricians and the Trades
#24730 - 04/22/03 03:03 AM Re: GFCI
zapped208 Offline
Member
Registered: 02/18/03
Posts: 196
Loc: Somewhere in USA
I treat it like a full size ground, and attach to all devices.
_________________________
Shoot first, apologize later.....maybe
Top
#24731 - 04/22/03 06:57 AM Re: GFCI
GEO Offline
Member
Registered: 03/12/03
Posts: 47
Loc: Lancaster,Pa
not sure of the question ? do you mean a/c (bx) cable , what type of boxes ? GEO
Top
#24732 - 04/22/03 11:44 AM Re: GFCI
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
LK,

Do you mean the smaller size ground wire that was in the older NM cables?
Top
#24733 - 04/22/03 02:37 PM Re: GFCI
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
LK:
In my opinion, a reduced size (wire guage) ground conductor is better than "no ground". The older NM cable had 16 gauge ground, and most of that cable was/is #14, for the hot and neutral conductors, and should be on a 15 amp OCP.

As an AHJ ion NJ, I would accept the undersized ground. For any arguments, I would fall back to "good old common sense", but as there is no NEC article for that, I would use the NJ "Rehab" Code out of the UCC (5:23 et al)

John
_________________________
John
Top
#24734 - 04/22/03 05:44 PM Re: GFCI
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
I find reduced grounds under cable clamps, twisted under sheet metal screws and pushed through holes in the box. None of these connections are good grounding practices.
When installing a GFCI I find it best to check all down stream ground connections.
It looks like everyone agrees reduced ground better then none at all.
LK
Top
#24735 - 04/22/03 06:38 PM Re: GFCI
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
Then of course a reduced ground will show a ground with your average tester, but may increase the resistance enough in the event of a fault to not trip the OCPD. In which case it would be better to mark the GFCI as "no equipment ground" so no one is deceived about the actual grounding ability of the circuit.
Top
#24736 - 04/22/03 08:19 PM Re: GFCI
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
Steve:
Good point this is why some type of marking should note the missing link. I have a problem finding a label NO EQUIPMENT GROUND the GFCI Mfg. should put them in the box. They have about 4 info sheets in there now.

LK
Top
#24737 - 04/23/03 03:48 AM Re: GFCI
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
LK,

Most GFCI manufacturers now include both labels in the box. (GFCI protected outlet, No equipment ground).
Top
#24738 - 04/23/03 07:09 AM Re: GFCI
rmiell Offline
Member
Registered: 11/09/00
Posts: 242
Loc: La Junta, Co. USA
In this situation, why is the existing (reduced) equipment grounding conductor better than none? The whole circuit is protected by a GFCI, which will trip faster than the breaker will, in the event of a ground fault. That is it's function. IMOI, I would think the reduced egc is equal to no egc. Don't use it.

If you are talking about a non-gfci protected circuit, then, yes the reduced egc is preferred to none.
_________________
Rick Miell
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals