#24486 - 04/14/03 08:16 PM Mind if we revisit inground pools?
electricj Offline
Member
Registered: 08/26/01
Posts: 10
Loc: Boston, MA, USA
Hi,
I’m sorry if this has been addressed before, but maybe this will help a new electrician sometime in the future,

A relative has recently asked me to wire her new in-ground pool. The contractor will dig the hole and says he will finish the pool in a week. She asked me to “wire” it and I said OK. The pool is to be 20 ‘x 40’

Now, I wired a couple of pools about 15 years ago and remember some of it was quite tricky, add this to the fact that the electrical inspector is notorious in this town, I am a little nervous.

What I remember is the #8 soft drawn copper all around the pool; bonding everything metal and terminating at the pump. I remember installing a receptacle against the pool house, which was within 10 feet of the pool.

I am trying to blow the cobwebs off. Here are my questions:

Am I required to install a receptacle near the pool?

What is the best way to do it if they are not having a pool house at this time?

She tells me the pool is done with “graphite” instead of iron rebar – do I need to bond the “graphite”?

Also she says they are thinking of the new fiber optic lighting – does this have a metal shell and/or do I need to bond and at what point?.

Lastly, I plan on bringing a ¾” pvc from the house to the pump and branching everything from there – is this a good method?

What would this work generally cost her if she had someone else do it for her?

Thanks for any help
Top
Work Gear for Electricians and the Trades
#24487 - 04/14/03 08:25 PM Re: Mind if we revisit inground pools?
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1081
Loc: Milwaukee, WI
Top
#24488 - 04/15/03 06:48 PM Re: Mind if we revisit inground pools?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
ElectricJ:

Your relative probably means "gunite"; not "graphite".

First off, get a copy of the NEC that is in effect in your area, and go to Article 680.

Next, are permits required in your area???

Bonding is pretty straightforward, any metal over 4 sq inches, within 5' of the pool must be bonded. #8 SOLID copper, bare or green.

Basically the wiring:
PVC, a conductor with a "W" (THHN/THWN)

Read Art 680, it's not that tough.
If the FO lighting has a metal shell, it has to be bonded, it may be a plastic shell.

Have you tried "speaking" to your AHJ??? All of them (us) are not bad guys.
John
_________________________
John
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 41 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals