#2446 - 07/10/01 04:17 PM GFI Connections
chrispatti Offline
Junior Member
Registered: 07/10/01
Posts: 6
Loc: Deltona,Fla. United States
Can someone please tell me the correct way to hook 2 GFI's and 1 regular 20amp duplex receptacle using one circuit in a commercial building. The regular duplex receptacle cannot be on the load side of the GFI's. The 2 GFI's are for the men and ladies restroom and the regular duplex receptacle is for an office. I always thought you needed a seperate neutral for each GFI you put in line on one circuit.
Top
Work Gear for Electricians and the Trades
#2447 - 07/10/01 04:23 PM Re: GFI Connections
Anonymous
Unregistered

>Can someone please tell me the correct way to hook 2 GFIs and 1 regular 20amp duplex receptacle using one circuit in a commercial building. The regular duplex receptacle cannot be on the load side of the GFIs.
So just pigtail them off your branch (parallel).

>I always thought you needed a separate neutral for each GFI you put in line on one circuit.
No such requirement technically or in Code.
Top
#2448 - 07/10/01 04:29 PM Re: GFI Connections
chrispatti Offline
Junior Member
Registered: 07/10/01
Posts: 6
Loc: Deltona,Fla. United States
So you are saying to just go to the line side of the GFI's when making my connections,then I do not need another neutral? Will the GFI's ever trip if they sense an imbalanced load in whatever is plugged into the regular receptacle?
Top
#2449 - 07/10/01 04:45 PM Re: GFI Connections
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Is this a multi-wire(2 or 3 hots and one neutral)circuit?
Top
#2450 - 07/10/01 04:55 PM Re: GFI Connections
chrispatti Offline
Junior Member
Registered: 07/10/01
Posts: 6
Loc: Deltona,Fla. United States
This is a single circuit application, 1 hot 1 neutral and a ground for 2 20amp GFI's and 1 20amp duplex receptacle.
Top
#2451 - 07/10/01 06:45 PM Re: GFI Connections
Anonymous
Unregistered

>So you are saying to just go to the line side of the GFIs when making my connections, then I do not need another neutral?
Correct.

>Will the GFIs ever trip if they sense an imbalanced load in whatever is plugged into the regular receptacle?[/B]
Not really. GFCIs are pretty clueless about the line side.
That's why they don't work if wired in backward (line and load interchanged).
Top
#2452 - 07/10/01 06:53 PM Re: GFI Connections
chrispatti Offline
Junior Member
Registered: 07/10/01
Posts: 6
Loc: Deltona,Fla. United States
Thank You for your help. So the only time you would need a seperate neutral for each GFI is if they are all feeding from seperate circuits?
Top
#2453 - 07/10/01 07:53 PM Re: GFI Connections
Anonymous
Unregistered

>the only time you would need a separate neutral for each GFI is if they are all feeding from separate circuits?
That is correct. But that is because separate circuits need their own (line-side) neutrals by Code. This is not a technical requirement for a GFCI to operate.

However, the load side current must not be diverted anywhere. In other words, if you cross your load-side neutral with any other neutral, the GFCI will trip. And if any load on the GFCI is not hooked to the load-side neutral of that same GFCI, then when that load is activated, the GFCI will trip.



[This message has been edited by Dspark (edited 07-10-2001).]
Top
#2454 - 07/11/01 05:56 AM Re: GFI Connections
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
There was a time when GFCI's first came into the market, and were required by the NEC, that separate neutrals were required to prevent nuisance tripping.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 90 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals