#24143 - 04/05/03 01:54 PM Romex?
rowdyrudy Offline
Member
Registered: 11/02/02
Posts: 169
Loc: Mascoutah, IL USA
A small local EC (buys from big boxes) brought me a section of wire for an opinion. The labeling is:GCC-K Romex 14/3 with ground Type NM-B 600 volts (UL) 6/27/01 #2173/2616.
The conductors are THHN but the insulation is thinner than some THHN that I have and there is no filler in the jacket. It is about 25% smaller overall than some 14/3 w/g that I have. Since I haven't been active in homes, is this normal now or is this an import from China?
Rowdy
Top
Work Gear for Electricians and the Trades
#24144 - 04/05/03 02:05 PM Re: Romex?
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
That's how all the 14/3 and other types of NM cable are made now. If it's from General Cable then it's American made. Although the actual copper could come from anywhere.

The "K" stands for Kingman, which was General Cable's Kingman, Arizona plant before it was sold to Southwire.

</totally useless information>
_________________________
Peter
Top
#24145 - 04/05/03 02:14 PM Re: Romex?
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Rowdy,

I'm not sure of the particular piece you have but I have noticed a real need to make sure that romex connectors (metal) are not tightened too much on these new 'thinner' cables. They seem to short very easily.

Bill
Top
#24146 - 04/05/03 02:20 PM Re: Romex?
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 914
Loc: Alpharetta, GA
The Southwire 14/3 is a lot tighter that the stuff my supply house sells ( usually General or Carroll). Same with all Southwire Romex. Even though it's smaller I've found it's tougher to pull than the old stuff. Don't know why though.
Top
#24147 - 04/06/03 08:02 AM Re: Romex?
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1081
Loc: Milwaukee, WI
Bill:
Quote:
...make sure that romex connectors (metal) are not tightened too much on these new 'thinner' cables. They seem to short very easily.


How common is it (among you pros out there) to test (with a continuity tester, etc.) before turning on the power? I agree that the newer cable jacketing is not very forgiving.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals