The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
1 registered (cableguy619), 212 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#23709 - 03/25/03 05:58 PM Capacity debate (what a circuit can handle)
LuminateME1 Offline
Member

Registered: 03/06/03
Posts: 25
Loc: Seattle,WA,USA
What can a 15 amp breaker hold (as far as watts). Also 20 amp--30 amp--and 40 amp. Heck we are in great debate over this issue. It's in the book, but many people have their own ideas. I know that we are to use only 80% of it's actual capacity. Example: Lets say a 15 amp breaker can handle 1800 watts max. I would then use only 80% of that capacity. So: 1440 watts would be the most I would put on that one circuit. Would love to hear you input. Heck, debate me down baby! LOL

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#23710 - 03/25/03 06:01 PM Re: Capacity debate (what a circuit can handle)
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
When you say, "What can a 15 amp circuit breaker hold?" What do you mean? What it REALY can hold? Or what you install on it? Most electricians use the 80% rule. (I believe)A 15 amp breaker can hold more than 15 amps, this way it can be used for the start up of motors and HVAC equipment.

Top
#23711 - 03/25/03 06:13 PM Re: Capacity debate (what a circuit can handle)
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
Now we are asking a "debate" question.....
IF it is an FPE 15 amp breaker (stab-loc) it may "hold" at 100 amps for a few.....it also may hold at 35 for a while......
A 15 will trip at the rated current based on the time curve calculated by the factory.

Harold is correct that a cb can "hold" to allow motor start-up, that is also based on the time curve.

You can obtain time curve info from the mfg's, and there is a lot of time curve info at Bussman Fuses.

John

The 80% rule is used.
_________________________
John

Top
#23712 - 03/25/03 06:14 PM Re: Capacity debate (what a circuit can handle)
LuminateME1 Offline
Member

Registered: 03/06/03
Posts: 25
Loc: Seattle,WA,USA
To clarify what I meant (sorry): What can a 15 amp breaker hold on a circuit being ran for a single family home dewelling. How many openings?

Top
#23713 - 03/26/03 03:07 AM Re: Capacity debate (what a circuit can handle)
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
A 15 amp breaker can be loaded up to 15 amps for Non-continuous loads.

For continuous loads no more then 12 amps (80%)

The code does not use 80% as the terminology they have you calculate a continuous load circuit at 125%, but the result is the same
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#23714 - 03/26/03 04:22 AM Re: Capacity debate (what a circuit can handle)
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Contrary to popular belief, the NEC does not limit the number of receptacle outlets on a residential circuit. However, many use the 180 VA rule which will result in 8-10 outlets (dpeending on if you apply the 80% rule) on a 15 amp ckt.
The other side of the argument is that the more receptacles you install, the less likely extension cords will be used.

Top
#23715 - 03/26/03 09:18 AM Re: Capacity debate (what a circuit can handle)
DBC1 Offline
Member

Registered: 03/15/03
Posts: 18
Loc: Tulsa, OK USA
I believe iwire has the correct answer. 15 amps for non continious, and 12 for continious.

Top
#23716 - 03/30/03 03:25 PM Re: Capacity debate (what a circuit can handle)
wocolt Offline
Member

Registered: 12/06/02
Posts: 117
{QUOTE]DBC1 --I believe iwire has the correct answer. 15 amps for non continious, and 12 for continious.{/QUOTE]
This is residential right ? where is there a continuous load...?
by definition continuous load is 3hours or more. Just askin'

WOC

Top
#23717 - 03/30/03 06:18 PM Re: Capacity debate (what a circuit can handle)
elecbob Offline
Member

Registered: 08/23/02
Posts: 142
Loc: WA
Whatever happened to 3 watts SQ/FT for receptacle and lighting loads in SFR's?
bob

Top
#23718 - 03/30/03 06:31 PM Re: Capacity debate (what a circuit can handle)
LuminateME1 Offline
Member

Registered: 03/06/03
Posts: 25
Loc: Seattle,WA,USA
to answer your question Wocolt. Yes, it's residential. Thanks for the responses!