The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#23053 - 03/10/03 12:42 PM ground cable
SJT Offline
Member

Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
We want to protect an insulated #6 THHN with 1/2" EMT instead of PVC. Will running an insulated ground wire through EMT choke the current if it does return on that wire? I know if it is bare, EMT should not be used.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#23054 - 03/10/03 01:55 PM Re: ground cable
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
If this is a grounding electrode conductor, it must be bonded to the EMT at both ends. See 250.92(A)(3)

If this is an equipment ground, generally speaking, it has no business being run outside of the raceway or cable that contain the circuit conductors.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#23055 - 03/11/03 05:54 AM Re: ground cable
SJT Offline
Member

Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
Thanks Tom,
The insulated #6 is for a jumper that will go from a satellite dish grounding conductor to the building electrode. To tie the two grounds together for article 810.21(J) Its one of those ground items that does not come up very often, but we want to do it to code.