We want to protect an insulated #6 THHN with 1/2" EMT instead of PVC. Will running an insulated ground wire through EMT choke the current if it does return on that wire? I know if it is bare, EMT should not be used.
Top
Work Gear for Electricians and the Trades
#23054 - 03/10/03 01:55 PM Re: ground cable
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
If this is a grounding electrode conductor, it must be bonded to the EMT at both ends. See 250.92(A)(3)

If this is an equipment ground, generally speaking, it has no business being run outside of the raceway or cable that contain the circuit conductors.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#23055 - 03/11/03 05:54 AM Re: ground cable
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
Thanks Tom,
The insulated #6 is for a jumper that will go from a satellite dish grounding conductor to the building electrode. To tie the two grounds together for article 810.21(J) Its one of those ground items that does not come up very often, but we want to do it to code.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals