The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 6 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#22983 - 03/09/03 03:15 PM Wiring size for a long run
ksan Offline
Junior Member

Registered: 02/23/03
Posts: 3
Loc: Gulf Breeze, Florida
I need to run 115 to a motor rated at 10.6 amps that is about 250 ft from the main service. The motor is the only thing on the circuit. Is 12 guage wire sufficient or should a smaller guage be used?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#22984 - 03/09/03 03:51 PM Re: Wiring size for a long run
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Using a voltage drop calculator I got on the Web and the info you gave you will have voltage drop of 10.5 volts or 9.2% if you use #12

#10s would be 5.5% drop or 6.3 volts
#8s would be 3.5% drop or 4.0 volts
#6s would be 2.2% drop or 2.2 volts
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#22985 - 03/09/03 07:26 PM Re: Wiring size for a long run
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Not wanting to throw a wrench in the gears, remember that for motors, one needs to also consider starting voltage drop. A rule of thumb for starting is 15% maximum. This is why 230 and 460V motors become attractive.

{Note that starting voltage drop is not a Code requirement, or even an FPN. Overlooking it can cause problems, and is commonly part of the commercial and industrial design process.}




[This message has been edited by Bjarney (edited 03-09-2003).]

Top
#22986 - 03/09/03 07:34 PM Re: Wiring size for a long run
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Bjarney, not a wrench in the gears but do you apply the 15% to the FLC, so 10.6 x 1.15 = 12.19 amps and then apply the voltage drop calcs. And does 15% work for all voltages.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#22987 - 03/09/03 07:54 PM Re: Wiring size for a long run
Edward Offline
Member

Registered: 12/14/02
Posts: 309
Loc: California
Check to see if you can wire it to 240 Volt
If you can then use 240 Volt connections and use 8 AWG wires.

Edward
_________________________
Thanks
Edward

Top
#22988 - 03/10/03 08:56 PM Re: Wiring size for a long run
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
ok i look at my electican calculator and for 115 volts appactions for that kind of distance i recomoned #10 is minumin wire size other wise if the moter can change to 230 volts. if so all by the mean go for 230 volts and i got one note from power company say any electric moter over 1 1/2 hp will like to keep on high side (voltage) due less stress at the transformer and line effcts and btw most motors dont like to start when voltage get too low ( i have alot of sevrvice call with waterwell pumps and came with way too small a wire size )


merci marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#22989 - 03/11/03 03:38 PM Re: Wiring size for a long run
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
iwire — Sorry for the slow follow-up. Motor starting current is usually something like 6xFLC.