#22825 - 03/05/03 01:30 AM Thermostats
Paxman Offline
Member
Registered: 06/03/02
Posts: 13
Loc: Woodinville, WA. USA
On a service call the other day I found a thermostat ( Caded model C2002, UL5C86, 240V, 22A max, single pole) that caught fire in the middle of the night. Luckily the owner was able to put it out. Somebody replaced one of the baseboards in living room with a 3,000W fan driven heater which increased the total load on the thermostat to 4,500W (or 18.75A )on a 20A circuit. I always load the heating circuits at no more than 80% or 16A in this case, but even 18.75A was well within the thermostat rating of 22A max. I tend to believe that the short happened in the electronic circuitry inside the thermostat ( poor heat dissipation? )
To make a long story short, the problems were corrected but I wander if anybody had similar experiences/what thermostats do you use?
Top
Work Gear for Electricians and the Trades
#22826 - 03/05/03 06:23 AM Re: Thermostats
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Do a web search on "recall of electric heating thermostats" and you will see some information that may apply
Top
#22827 - 03/05/03 07:38 PM Re: Thermostats
nesparky Offline
Member
Registered: 06/21/01
Posts: 642
Loc: omaha,ne
22A x .80 = 17.6A Alternatly 18.75A x 1.25 = 23.4375A
Either way the thermostat became too small when the new heater was installed.
Of course the circuit is now also too small for the load.
Good luck with the fix.
_________________________
ed
Top
#22828 - 03/08/03 07:12 PM Re: Thermostats
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Paxman,
I would side with nesparky on this one,
but, the person who changed the heaters over, should have checked this before-hand!.
I have had Thermostats burn-out on me before, but not as destructively as that, it must be the internals that got way too hot.
There was nothing blocking the small vents on the Thermostat, was there?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#22829 - 03/09/03 12:14 AM Re: Thermostats
Paxman Offline
Member
Registered: 06/03/02
Posts: 13
Loc: Woodinville, WA. USA
Hey, it could've been one of those "handyman special" type job... which reminds me of another situation I found while doing a service change - a handyman installed a 3,000W heater in each bedroom and then slapped in a 30A breaker because the 20A one kept tripping. Talk about a fire waiting to happen.
In this case I did replaced the other two thermostats in bedrooms because they also showed signs of overheating. Vents were not obstructed by anything.
Top
#22830 - 03/09/03 10:25 PM Re: Thermostats
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Good point mate,
I only use quality Thermostats(Honeywell).
If you are ever in doubt, about a Thermostat,
use it to switch a Contactor, at the Switch-board.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#22831 - 03/22/03 01:25 PM Re: Thermostats
Weyfer Offline
Junior Member
Registered: 10/14/02
Posts: 3
Cadet manufacturing;specialising in keeping the fire departments busy
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals