The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
0 registered (), 107 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#22797 - 03/04/03 06:45 AM Motor Question
rayb Offline
Junior Member

Registered: 02/18/03
Posts: 7
Loc: Carlisle, MA USA
Hi All,

I have a Westinghouse 'Lifeline A' motor, 215 frame, mod ABDP, 5HP, 3 PH, 240/480 V, 1725 RPM motor. Can anyone give me the wiring diagram for this thing?


Ray Bahr

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#22798 - 03/04/03 09:05 AM Re: Motor Question
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA

#22799 - 03/04/03 09:29 AM Re: Motor Question
gramps Offline

Registered: 08/25/02
Posts: 120
Loc: ohio
since you indicate that its a single-speed, dual voltage motor, it probably has 9 leads coming out of it, although, it could possibly have as few as 6, or as many as 12. please let me know how many leads it has coming out, and any designation markings on each lead. is it an IEC motor, or a NEMA motor? it should say, one or the other on the nameplate.

if its a 6 lead NEMA motor, it can be WYE connected for high voltage,(480), or DELTA connected for low voltage (240). the connections for this type of motor are as follows:
high---L1/1, L2/2, L3/3----and 4,5,6 tied together.

if its a 9 lead NEMA motor, it can be connected as follows:
wye-connected high---L1/1, L2/2, L3/3----4&7 joined--5&8 joined--6&9 joined
wye-connected low---L1/1&7, L2/2&8, L3/3&9----4,5,6 tied together
delta-connected high---same as wye-connected high
delta-connected low---L1/1,6,7--L2/2,4,8--L3/3,5,9

it is probably one of these configurations. if it is in fact, a 12 lead motor, please let me know and i'll post the wiring configurations for it separately, as the 12 lead config. is a little more involved, and theres not much sense in taking up space here posting it, if you dont need it.

also, let me know if its an IEC motor, and not NEMA, although i think, from your information, its probably NEMA.

hope this helps.


#22800 - 03/04/03 10:39 AM Re: Motor Question
rayb Offline
Junior Member

Registered: 02/18/03
Posts: 7
Loc: Carlisle, MA USA
Thanks folks,

I think this covers it!


#22801 - 03/04/03 07:07 PM Re: Motor Question
electric-ed Offline

Registered: 07/08/02
Posts: 184
Loc: Canada
Ray, if it is a standard 9-lead, 3 phase motor, it will be either wye or delta wound, but not both.

You will have to know which it is, because if it is wye-wound, is won't operate properly with the windings connected delta.

You can easily determine that with any continuity tester.

The NEMA 6-lead, 3 phase motor could be either a two-speed motor or a single-voltage motor designed for use with a wye-delta starter.

More Winding connection charts here.


[This message has been edited by electric-ed (edited 03-05-2003).]