#22666 - 02/26/03 09:18 PM Must I replace a single 15-amp receptacle on a 20 amp ckt. with a 20 amp receptacle?
SvenNYC Offline
Member
Registered: 08/19/02
Posts: 1685
Loc: New York City
There is a 15 amp (single) receptacle on a 125 volt-20 amp dedicated circuit in an apartment.

This receptacle replaced a heavily paint-glopped 20-amp receptacle. (I didn't realize what it was until I picked up the pieces off the floor - by then it was too late to get a 20-amp 125volt device).

It only powers a 110-volt 15-amp air conditioner in the summer and during the winter it occasionally powers some light appliances like lamps, X-mas tree lights and the occasional television set.

Considering all of the above, must I replace this 15-amp receptacle with a 20 amp device? Or is it OK to leave it as is for the time being?
Top
Work Gear for Electricians and the Trades
#22667 - 02/26/03 09:43 PM Re: Must I replace a single 15-amp receptacle on a 20 amp ckt. with a 20 amp receptacle?
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2342
Loc: West Virginia
Sven,

It is actually common and permitted to install 15A Receptacles on 20A circuits, provided there is at least one duplex (or two singles) on the circuit.

This is assuming #12 wire, of course.

_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#22668 - 02/26/03 10:06 PM Re: Must I replace a single 15-amp receptacle on a 20 amp ckt. with a 20 amp receptacle?
SvenNYC Offline
Member
Registered: 08/19/02
Posts: 1685
Loc: New York City
Virgil,

Thanks very much. I forgot to mention. This is the only receptacle on that circuit. It is supposed to be a dedicated air conditioner circuit for a maximum 20-amp/125volt unit.

So judging by what you said, the existing 15-amp socket should be replaced by a 20-amp, correct?
Top
#22669 - 02/26/03 10:10 PM Re: Must I replace a single 15-amp receptacle on a 20 amp ckt. with a 20 amp receptacle?
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2342
Loc: West Virginia
That would be the best thing to do, given it is a single dedicated receptacle. In a pinch, a duplex would be legal even if the second receptacle is not used, but considering the expected load, a single 20A Spec grade would be my recommendation....
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#22670 - 02/27/03 04:31 AM Re: Must I replace a single 15-amp receptacle on a 20 amp ckt. with a 20 amp receptacle?
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
If this is a SINGLE receptacle that is fed from a dedicated 20 amp circuit it MUST be a 20 amp rated receptacle.
Top
#22671 - 02/27/03 06:12 AM Re: Must I replace a single 15-amp receptacle on a 20 amp ckt. with a 20 amp receptacle?
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2342
Loc: West Virginia
Apparently I failed to make myself clear and managed to look like an idiot.

To reiterate:

Single receptacle: MUST be a 20

Duplex Receptacle: 20 or 15 is OK

Multiple Receptacles: 20 or 15 is OK

Better?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#22672 - 02/27/03 06:26 AM Re: Must I replace a single 15-amp receptacle on a 20 amp ckt. with a 20 amp receptacle?
SvenNYC Offline
Member
Registered: 08/19/02
Posts: 1685
Loc: New York City
Thanks very much Virgil and 'Scott!!!!!

You both cleared it all up.

[This message has been edited by SvenNYC (edited 02-27-2003).]
Top
#22673 - 02/27/03 06:59 AM Re: Must I replace a single 15-amp receptacle on a 20 amp ckt. with a 20 amp receptacle?
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
All egos checked at door! Just trying to help clarify.

[This message has been edited by Electricmanscott (edited 02-27-2003).]
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals